I have let a flat for a several years to the same person (not a new tenancy). Hall, kitchen, bathroom, two bedrooms and lounge. All on one floor.
Letting agent sent electrician to do EICR and it came back 'unsatisfactory':
Part 6: Observations and recommendations (all are Code C2)
1. 4.9 The main switch RCD did not trip when test button pressed.
2. 8.6 The cover of the lighting fitting is missing in the bathroom and needs replacing.
3. 8.7 The cover of the lighting fitting is missing in the bathroom and needs replacing.
4. The cable feeding the lighting circuit has no CPC, the lighting circuit needs to be rewired.
5. The metal switches have not earthed in the back boxes.
6. Circuits 4, 6 and 7 have multiple cables in the MCBs. These need to be put in their own MCB no spare ways.
Part 12: Circuit details
RCD
1. Cooker
2. Shower
3. Kitchen sockets
4. Sockets
5. Immersion heater
6. Sockets
7. Lights
8. Sockets
The agency's preferred electrician (whose company did the EICR) has quoted:
There are seven lights (two in lounge). While surface wiring wouldn't be my choice, I appreciate it is much quicker and easier than chasing out and making good.
Do you agree with the codes and is the quotation reasonable?
If not, does anyone local (Nottingham) want to quote?
Thank you.
Letting agent sent electrician to do EICR and it came back 'unsatisfactory':
Part 6: Observations and recommendations (all are Code C2)
1. 4.9 The main switch RCD did not trip when test button pressed.
2. 8.6 The cover of the lighting fitting is missing in the bathroom and needs replacing.
3. 8.7 The cover of the lighting fitting is missing in the bathroom and needs replacing.
4. The cable feeding the lighting circuit has no CPC, the lighting circuit needs to be rewired.
5. The metal switches have not earthed in the back boxes.
6. Circuits 4, 6 and 7 have multiple cables in the MCBs. These need to be put in their own MCB no spare ways.
Part 12: Circuit details
RCD
1. Cooker
2. Shower
3. Kitchen sockets
4. Sockets
5. Immersion heater
6. Sockets
7. Lights
8. Sockets
The agency's preferred electrician (whose company did the EICR) has quoted:
- To isolate and remove old consumer unit replace with a new dual RCD consumer unit as per regulations.
- To rewire the lighting circuit in the property (the cables will be run in surface trunking and the switches will be mounted on surface boxes to reduce damage to the walls and decorating).
There are seven lights (two in lounge). While surface wiring wouldn't be my choice, I appreciate it is much quicker and easier than chasing out and making good.
Do you agree with the codes and is the quotation reasonable?
If not, does anyone local (Nottingham) want to quote?
Thank you.