Hi Folks
This is my first post, but I've been reading many posts over the last few months and have found this forum very informative and some times very humorous, Thank you all.
I have recently come across a problem whilst doing some PAT testing for a customer that has left me confused. Although this is nothing to do with PAT testing it was my PAT testing meter that highlighted the problem when I plugged it into a socket.
The property is a 4 year old Timber barn and the loft has a small ring circuit with a spur off it feeding a socket below for a small telly.
My problem is that all of the sockets are only giving voltage readings of 60v but the reading for the circuit at the CU is the standard 240v
The only thing that I can think of is that when building the property someone has banged a nail through a cable somewhere.
I have been round all of the sockets and checked connections etc and found nothing obviously wrong.
When I mentioned it to the customer he said don't worry its probably been like it for ever and the sockets only supply low voltage stuff anyway.
Well I am concerned that its wrong and there is possibly a nightmare waiting to happen.
Im thinking of contacting the customer and trying to get him to let me rectify the problem
Is there anything else it could be?
I await your reply's with baited breath :)
Nothing is impossible, but could be highly unlikely. Depending on the input range of switch mode power supplies it could be possible for electronics to function, but that does of course assume that this measured voltage is the open circuit voltage and not the result of a load in series with a high resistance connection.
Yep open circuit
Yep open circuit
How many threads I have read where voltage readings(regrettably sometimes with the wrong instrument)have been noted on an installation and all sorts of sometimes wild claims are made by the operator
Concentrating the mind on voltage readings and assessing the safety of an installation on those readings is a sure fire way of coming to wrong conclusions
There are better and tried and tested means of making the assessment of the safety of an installation
Those who are unsure of how or what to test,they are the usual culprits for not being aware that wrong assumptions can be made
I suggest refraining from condemning work based solely on voltage readings,that is until the proper safety tests confirm there actually is a problem
Reply to Large Volt Drop in ring circuit in the UK Electrical Forum area at ElectriciansForums.net
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Seen this where T&E has been fixed with a flat bend of too tight a radius.