Learning electrical motors | on ElectriciansForums
Discuss Learning electrical motors in the Talk Electrician area at ElectriciansForums.net
Liverpool
Hi, I’m Not getting enough torque on startup to turn pump. Turns pump successfully maybe 1 in 6 times on startup and then fine at full speed. Currently connected in star as per plate, 400V. Ran from a three phase inverter. Should this be wired delta? Still very much learning.
  • [ElectriciansForums.net] Learning electrical motors
A VSD then. if it says 230V in and 400V out then the motor should be connected star.
This is a bit more of an 'upmarket' VSD than the ones I have used, but on the cheaper ones there's loads of parameters to set up.
Most single phase Input vsd have a 3 phase output of 230v between phases.
therefore a delta connection at the motor would be correct.
Is this inverter being fed from a 400v 3 phase supply?
if not then what is it being supplied with?
Reply to Learning electrical motors in the Talk Electrician area at ElectriciansForums.net
Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...