on a lecsoft simulator I came across this...

When working on a construction site, the result of the resistance of the earth electrode and the rated residual operating current should not exceed

a)110v
b)50v
c)25v
d)230v

i put 110v not really understanding the question... but the answer was 25v confused.com
 
50V touch voltage is the answer. that's why the max. Zs for an RCD protected circuit is 1667. ( 1667 x 0.03 = 50V ).
 
Upvote 0
nicked this from iet

--------

Construction sites are governed by section 604 of BS7671.

The normal 7671 regs apply inside the site hut and you can use the TNCS (PME) supply. It is a good idea anyway to protect the installation with a 30mA RCD.

The 4 double sockets you mention " on a site board". Hopefully this is not outside as this is not permitted. Portable tools have to be plugged in to 110V centre tapped transformers.


You cannot take the PME supply outside so you will have to TT it separating the supply earth and putting in an earth electrode.

The earth loop impedance values for TN systems are listed in in 604 for various voltages for 0.2s. These only apply to TN systems. If you are using an RCD these do not apply. The maximum touch voltage is reduced to 25V so the resitance of the earth electrode (Ra) mutilpied by the operating current of the RCD must be equal to or less than 25V. The 110V loop impedances can be tested with some loop impedance testers if they will go down to 110V.

If the REC will not supply without a certificate then you will have to limit the test to " no supply available dead testing only further testing required when supply is connected". I have done a number of these to get a supply re-connected to houses on change of occupancy. Re test when the supply is connected. Use the normal certificates.

The interval for testing construction sites is 3 months.

Does this help?

Regards

John Peckham

-------------------------
John Peckham
 
Last edited:
Upvote 0
have a look at swindon massive it isis better as it explains why so you can research it yourself.

because of how the 110v transformers work.

50v phase to earth
110v phase to phase

I totally agree with ya and i understand about 110V transformers 50V to earth but why has the op stated the answer was 25V thats not the correct answer is it
 
Upvote 0
seem to have in back of brain that max. touch volts on building site used to be 25V, but is now 50V.
thats because the example i chose was TN and you chose tt

the max touch voltage is ohms / disconnection time

for tt thats 1667 ohms allowed for electrode resistance

50 / 0.03 = 1667

1667 / 30ma = 50v touch voltage

ohms / rcd rating = touch voltage

i think thats where they are getting the touch voltage from

feel free to correct/ tell me im an idiot but this is what ive just researched
 
Last edited:
Upvote 0
thats because the example i chose was TN and you chose tt

the max touch voltage is ohms / disconnection time

for tt thats 1667 ohms allowed for electrode resistance

50 / 0.03 = 1667

1667 / 30ma = 50v touch voltage

ohms / rcd rating = touch voltage

i think thats where they are getting the touch voltage from

feel free to correct/ tell me im an idiot but this is what ive just researched


You may or may not be an idiot, but you're certainly confused.

"the max touch voltage is ohms / disconnection time"

Disconnection time isn't relevant here; I'm guessing you really mean rated residual operating current.

Now go back to basics: V=IxR, not R/I
 
Upvote 0
You may or may not be an idiot, but you're certainly confused.

"the max touch voltage is ohms / disconnection time"

Disconnection time isn't relevant here; I'm guessing you really mean rated residual operating current.

Now go back to basics: V=IxR, not R/I
[ElectriciansForums.net] lecsoft weird question
 
Upvote 0
nicked this from iet

--------

Construction sites are governed by section 604 of BS7671.

....................................

I think the OP's question is well out of date!

Shanks, you need to ensure your research is upto date, 604 is the obvious giveaway! :smilielol5:


The 25V and 0.2s were dropped with the introduction of the 17th (see page 6 BGB), so the answer is 50V.
 
Upvote 0
cheers archie for confirming what i said in post#2. apart from eng54's post and 1 or 2 others, several posts have been absolute bollox.
 
Upvote 0

Reply to lecsoft weird question in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

  • Question
Hi Seems that this is an out dated question and the above would have been correct in the 17th edition. Thanks for the reply
Replies
11
Views
2K
  • Question
Ah OK, that makes sense. Thank you Avo.
Replies
12
Views
2K
  • Question
Yeah I doubt it's normally an issue. Split load boards and SWA incomers are likely the only trouble.
Replies
16
Views
3K
i would split he tails and fit an additional 2/3 way CU to supply the garage/whatever. that way you could feed in SWA, installung RCDs as and if...
Replies
3
Views
4K
yeh thank you guys, came across this last night, i knew it was a mess but sometimes you start to second guess yourself lol
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks