I went out to a property today and the tenant had 6 down lights connected to a 3 way switch system. The down lights worked great! When the tenant installed LED bulbs there seemed to be a dim glow from the bulbs. The bulbs are 240V 2W. When the switches are off there is 47V at the fittings.
Can anybody help with this one???!!!!!
 
This phenomenon is caused by the final circuit cable capacitance. It is more common in conventionally wired two way and intermediate switching circuits due to the wide spread use of 3+E cable and the extra parallel capacitance that creates. LED lamps are particularly sensitive to this because they require very little current to drive the lamp.
The mains LED lamp is essentially a number of LEDs driven by a constant current driver powered by a mains rectifier and smoothing capacitor.
Even though the live feed to the LED lamp is switched OFF the cable capacitance allows leakage current to flow to the lamp slowly charging the smoothing capacitor in the lamp until the potential is sufficient for the constant current driver to "fire" the LEDs. This discharges the smoothing capacitor, the constant current driver stops, the LEDs extinguish and the process of charging starts again ... if conditions are suitable this continues indefinitely.
If the charge/discharge cycle (repetition rate) is short, the LEDs appear to be 'ON' continuously, however the energy is limited so the LEDs are only barely lit.
If more lamps are added to the final circuit the loading on the cable capacitance can be such that the individual smoothing capacitors of some or all of the lamps do not reach "firing" potential. Or you may find that only one or a few lamps on a circuit are effected due to the distribution of the cable capacitance and the manufacturing tolerances of the lamps. This can be quite disconcerting the first time you encounter it.
A tungsten filament lamp doesn't suffer this problem because the filament is permanently loading the cable capacitance and any acquired charge is unable to overcome the thermal inertia.
A simple solution is to permanently discharge the cable capacitance by wiring two 160K ohm, 1/4W, resistors rated at >=250V, in series across L and N on the final circuit, it is good electronics practice to do this as close to the effected lamp as possible, if this is done across the switched L and N at the lamp holder terminals it allows simple switching out of circuit (or disconnection) for testing. Do not try to use a single 330K ohm resistor because this may fail due to voltage breakdown.
If the final circuit has a large number of switched lamps it may be pragmatic to connect the series resistors between permanent L and N at a convenient point e.g. at the DB to reduce the number of resistors required, however the number of points that will require treatment will depend on how the cable capacitance is distributed on the final circuit. Additional points particularly where 3+E is used for 2 way and intermediate switching may well require additional pairs of resistors.
If this solution is implemented a notice should be placed at the DB stating which final circuits are effected and how they have been modified.
 
Last edited by a moderator:
I had this problem on a kitchen lighting circuit.
i fitted a 400v 0.1uf capcitor across the switchline and neutral at the light fitting problem solved for me.
worth a go ÂŁ2.87 from maplins.
 
Thanks for that. Some really good technical advice. What would I do if there is 6 effected down lights that are dimly glowing? (on the same 3 way switch) Sorry if that sounds thick!

The solution is cheap enough that you can afford to do all 6 lamps if necessary, but normally you'll have to do less than half of them. Do a lamp at a time, functional test after each modification, until the problem disappears. I would choose the last lamp on the final circuit, then if required a lamp near the middle of the circuit and if required then the first lamp on the circuit, etc. Usually I find one pair of resistors is all that is required.
 
Last edited by a moderator:
a snubber is, afaik, a combination resistor/capacitor which is wired L/N or SL/N, as said above, trial and error as to where and how many you have to fit.
 

Reply to LED bulbs Dim glow!!!! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

  • Question
Thanks davesparks. Looking at the diagram on the driver that's what I interpreted too, but I heard somewhere that the DALI system doesn't like...
Replies
2
Views
546
My experience with commercial lighting is when the fixture is ordered or bought the specs should say 120/277. Then their wiring diagram should be...
Replies
7
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top