G

Guest154

hi having some problems with led floodlight , firstly had 17 140w led floodlights on one circuit wired with a 10mm single line swa , started with 16 amp mcb and it kept tripping on start up not every time , tested all the cabling and and put the clamp meter on it cuming up with just over 10 amps on start up , so i changed the mcb to a 20 amp still tripping then a 32 still tripping finally a 40 amp mcb and it has stopped tripping , i then used the same floodlights on another 2 jobs 1 with 4 on a circuit and the other with 12 on a circuit and the same thing happened had to keep uppin the mcb , they are not cheap fittings ÂŁ400 a piece , i did contact the company that make them but the say they have had no issues like this b4 , anyone have any ideas
 
about 60 metres long , it was incase the leds were no good , would change the fittings to M-H fittings , yes even tryed a type d mcb , but there doesnt seem to be a high start up current
 
Is it the RCD going or the MCB. If its the MCB its quite likely that the "start up" current of the LED lights is taking more than the MCB can handle. As tel suggests can you try a type c?
 
Trying to get my head around this, not sure i'm right!
For simplicity you would need to look at the 4 floodlight setup. If this can trip at 32A C MCB which has a 0.1S trip at between 10 & 20 times the rated current i.e 320A minimum you are looking at 80A start up current per lamp! You said you used single line SWA, did you use this on all the problem installations? Personally I would do a mock up installation with several lamps & do some careful fault finding.
 
you say you have the same issue on 3 sites, but have a different number of lights at each, and have had to up the mcb.
so what size mcb and swa are you using on each currently?
 

Reply to led floodlight problems in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
1K
  • Question
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
2
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top