hi having some problems with led floodlight , firstly had 17 140w led floodlights on one circuit wired with a 10mm single line swa , started with 16 amp mcb and it kept tripping on start up not every time , tested all the cabling and and put the clamp meter on it cuming up with just over 10 amps on start up , so i changed the mcb to a 20 amp still tripping then a 32 still tripping finally a 40 amp mcb and it has stopped tripping , i then used the same floodlights on another 2 jobs 1 with 4 on a circuit and the other with 12 on a circuit and the same thing happened had to keep uppin the mcb , they are not cheap fittings ÂŁ400 a piece , i did contact the company that make them but the say they have had no issues like this b4 , anyone have any ideas
what was it sayin about start up current murdoch
That some LED lights have extremely high start up currents.
Edit:
Lamp ............................................ Peak Inrush Current ... Steady Current ... Real Power ... Apparent Power ... Power Factor
50W GU10 Halogen ..................... 2200mA ...................... 222mA ................ 53.4W ........... 53.4W ..................... 1.0
LEDlite 4.9W GU10 LED ................ 416mA ...................... 355mA .................. 5.9W ........... 53W ........................ 0.11
Halolite 1.5W GU10 LED (old) ...... 2100mA ........................ 23.4mA .............. 1.04W ........... 5.7W ...................... 0.18
LEDLite 10.5W LED downlight ........ 420mA ........................ 54.6mA ............ 11.6W ........... 13.2W ...................... 0.87
apologies to the chap who did this but I'm sure he won't mind me plagerising it!
clamp meter is only showing just over 10 amps on start up
Is this with a peak hold function or are you just catching the max reading visually?
(The investigations into LED start up currents and power factors were mine on another board.)
Somewhat related, I ended up putting three LED drivers for under-cupboard LED strip lights onto a 6A type C MCB as the inrush was sometimes measuring 50A for each driver on startup.
hi andy , contacted the company that sell them again but they say they have had no issues like this with these lights , not sure if i believe them but they are holding for now , i can only assume that these guys are right about the start up current being so high , next time i am on the sites i will try the clamp meter on them again using the peak hold function see what it comes up with , cheers
Reply to led floodlight problems in the UK Electrical Forum area at ElectriciansForums.net
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...