UPDATE -

After measuring voltages both by analogue and digital tracking across the main incoming bus bars and seeing as much as a 20v drop from only 4 or 5 amps of load, flagged it to the DNO who came out last week, looked at their connections, HV fuses etc and went away to arrange for an engineer to fit a quality analyser for a week so that they could look at it.

Today though, an inspection team arrived to do a pre-visit for changing the pole transformer at their cost - hurrah! I'd been under the impression that it was a 16Kva set, but they told me it was only a 5! So that explains a lot, and the calculated diversity on the installation is something like 220A due to a heat pump and private water treatment works. Anyway, they're going to fit a 25Kva at no charge (and change the 80A to 100A). Have to say, I like Western Power as my area DNO, they're really great to work with.
 
Other possible area's are load sharing of transformer with neighbours, size of transformer as a borderline transformer with struggle when heavy loads are switched on or high inductive loads thus effecting voltage but these issues with have to be taken up with the DNO

Glad you sorted it at no expense but hey! brownie point my way it was on my list :wink5:
 

Reply to LED lighting dropping out under circuit load in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
191
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Loose neutral somewhere… possibly at panel or at the last light before it goes to panel. You say you’re getting power through the switch and up...
Replies
1
Views
293
Thanks little spark. Good point but the drivers I'm considering have a sync and communication between driver function. So (as long as it works)...
Replies
6
Views
732

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top