UPDATE -

After measuring voltages both by analogue and digital tracking across the main incoming bus bars and seeing as much as a 20v drop from only 4 or 5 amps of load, flagged it to the DNO who came out last week, looked at their connections, HV fuses etc and went away to arrange for an engineer to fit a quality analyser for a week so that they could look at it.

Today though, an inspection team arrived to do a pre-visit for changing the pole transformer at their cost - hurrah! I'd been under the impression that it was a 16Kva set, but they told me it was only a 5! So that explains a lot, and the calculated diversity on the installation is something like 220A due to a heat pump and private water treatment works. Anyway, they're going to fit a 25Kva at no charge (and change the 80A to 100A). Have to say, I like Western Power as my area DNO, they're really great to work with.
 
Other possible area's are load sharing of transformer with neighbours, size of transformer as a borderline transformer with struggle when heavy loads are switched on or high inductive loads thus effecting voltage but these issues with have to be taken up with the DNO

Glad you sorted it at no expense but hey! brownie point my way it was on my list :wink5:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Rockingit

Mentor
Arms
Supporter
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
LED lighting dropping out under circuit load
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
Rockingit,
Last reply from
Darkwood,
Replies
16
Views
2,454

Advert

Back
Top