Just looked and it recommends 5 - FFS! And yes I ballsed up - was meant to write MCB in the title
Looks like you'll need to split the circuit then.
 
if the op has replace the 10 for led why would he put and a splitting them to a different circuit . he must have a fault on one of the lap C88p gear .
See his response In post #10, manufacturers recommend five fittings per circuit.
 
I suspect that the new LED lighting has a high crest factor, where Crest factor is the peak amplitude of the waveform divided by the RMS value of the waveform. So when a number of new LED fittings are supplied by the original mcb the electromagnetic functionality of the mcb detects the high total peak current and trips the breaker. The rms value is low and therefore there is insufficient Ohmic heating to cause the thermal functionality of the mcb to operate.

This is why there is a limit on the number of LED fittings per mcb size - you mentioned 5. I suggest you modify the wiring to power the lighting from 2mcbs, 5 LED strips on each. Or a higher current mcb if the wiring allows to power all 10 but this is not to be preferred.

[ElectriciansForums.net] LED'S keep tripping the RCD when switched off?
 

Reply to LED'S keep tripping the RCD when switched off? in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
692
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
784
Build up of Earth leakage from multiple machines and the planner just tipped it over the edge?
Replies
7
Views
292

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top