^^ OK lets use 30W as the under cupboard lights - so best option would be to disconnect 1 lamp or transformer to see if it improves.

Wonder how many other lights are on the circuit? How many are on when it trips?

My pennies are on inrush currents...
 
Thanks for the replies.
Apologies been really busy, I haven't been back to the property yet, the drivers are Ngl uk ltd, input 1 amp and output 3 amp, I have no other information about them.
The circuit trips only when the under cabinet lights are o and no other lighting.
I am thinking it is the In rush current as it doesn't happen all the time and it is when they are switched on, not when they have been on for a bit.
 
A suggested solution: Buy some Negative Thermal Coefficient (NTC) Thermistors and insert one in series with the line feed to the LED driver. See:

ntc thermistor | Rapid Online - https://www.rapidonline.com/Catalogue/Search?query=ntc%20thermistor&filterSearchScope=1&tier=NTC%20Inrush%20Limiters

Install the NTC thermistor inside a suitable non-flammable enclosure with the thermistor not touching the sides.

An NTC thermistor has a negative thermal co-efficient which means at low temperature (eg ambient) its resistance is high, but as current flows through it and ohmic heating occurs its resistance decreases to a low value. For example for a 2A thermistor its resistance is 50Ω at zero current and at 2A 0.8Ω. At 2A and operating temperature the volt drop will be 1.6V and the power dissipated is 3.2W. See link and technical specifications and data sheets. You might want to do a trial first.

Instead of inserting the thermistor in the line feed you could also try inserting one in series with a pole of the LV output side or perhaps one in series with the feed to each LED luminaire. The former is probably a better idea because the latter might result in uneven brilliance from the luminaires.
 
Last edited:
A good idea that @marconi. I had a lot of trouble with a load of Meanwell LED drivers in the past for external floods.
That trick may have saved me a load of a headache, and eventually needing a 16A D type for a 1 Amp load (Fortunately the numbers just worked out.. but it had me sweating).
 

Reply to LEDs tripping type 2MCB! in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

Neutral and live
Replies
2
Views
403
Thank you for your quick and excellent response - I hadn't thought about the cables changing over time. I'll replace all three. Thank you once...
Replies
2
Views
607

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top