@Pete999 have you not heard of Ductor testing?
High current low resistance testing.
Megger DLRO is a very common unit.
Mine is only 10A, but they are available up to 600A they stress the conductors to a higher level than the low current testing done by a typical MFT, or DMM.
They also offer a resolution much higher than those given by a typical MFT.
The way that EN 60204-1 is worded it is easily interpreted to require high current testing for all protective conductor networks.
A classic use for a Ductor was to test steel conduit when installed and utilised as the circuit cpc.
Very similar concept to the high current test used in PAT.Sounds like the high current earth bond test offered by some of the more expensive 'PAT' testers, including my fairly vintage Seaward one which does 25 amp low resistance testing.
Is ductor a trade name like Megger?
Very similar concept to the high current test used in PAT.
Ductor isn't a trade name AFAIK.
They are also known as I said above as high current low resistance testers, or micro/milli Ohmeters.
Megger DLRO10HD, DLRO200, Chauvin Arnoux CA6240/6255/6292 for example.
I have the DLRO10HD.
I have heard of Ductor testing, although I have never had the opportunity or experience of operating such a tester, was only asking out of interest.@Pete999 have you not heard of Ductor testing?
High current low resistance testing.
Megger DLRO is a very common unit.
Mine is only 10A, but they are available up to 600A they stress the conductors to a higher level than the low current testing done by a typical MFT, or DMM.
They also offer a resolution much higher than those given by a typical MFT.
The way that EN 60204-1 is worded it is easily interpreted to require high current testing for all protective conductor networks.
A classic use for a Ductor was to test steel conduit when installed and utilised as the circuit cpc.
I have heard of Ductor testing, although I have never had the opportunity or experience of operating such a tester, was only asking out of interest.
They are a 4 wire bridge measurement type device, so they automatically "null" out the lead resistance and you can even use them with two 50m wander leads within limits.Those testers look like they have an amazing level of accuracy. Reminds me of the short circuit location testers we used to use on circuit boards.
I always thought that as it started as "Con_ductor_ Tester", it was ductor, rather than "Con_ductor Tester_".I have a vintage one (naturally). I think the actual trade mark is 'Ducter' with an 'e', which is registered to Megger having started out as an Evershed and Vignoles product around the same time as the Megger.
YesHang on - does this mean that if you only connect to one earth terminal the other socket is not earthed for any appliance plugged into it?
Anyone had a word with CEF?
Interesting idea that I can kind-of believe. There was a strap across the back that was snapped off and lost during reverse-engineering of the original, and never made it onto the bill of materials for manufacturing the clones. But then, it seems unlikely that the original would have had two terminals. It's just odd.
If one leg of the CPC was placed in one terminal and the other leg in the other terminal the CPC would not be continuous. If both legs of the CPC were terminated into one terminal the other side would be unearthed, not good when using class 1 equipment.Two earth terminals is fairly common on 2 gang sockets these days, so the jury is out in my mind.
If one leg of the CPC was placed in one terminal and the other leg in the other terminal the CPC would not be continuous. If both legs of the CPC were terminated into one terminal the other side would be unearthed, not good when using class 1 equipment.
If placed at the end of a radial circuit then one side would remain unearthed.
If the socket was fitted to a metal backbox then the risk would be reduced but as most boxes have a floating lug then continuity cannot be assured.
The above scenarios are based on DIY installation where testing is very rarely carried out.
Bit of a no brainer for me, I wouldn't install one and would strongly advise a customer to remove it if I saw one fitted.
Only testing will tellI get the issue with the socket in question, but that issue is separate to the point I was trying (or rather failing) to make.
It was pointed out that CEF is selling a similar product and the implication was that their product would similarly be affected by this earthing issue. This raised the question in my mind whether this was a poorly designed product from one manufacturer, being sold under several brand names, or if there is a good quality original that has been badly copied by someone more concerned about profit than attention to detail.
Only testing will tell