I've ordered the cheaper one, lets have a look tomorrow.
Edit: I also forgot to say on my earlier post, if one of these was installed at the start of a radial circuit the other accessories would be left with no earth.
Also a metal backbox would not be earthed as it appears to have no earth contact with the fixing screws.
Hi Pete, I'm not an installer so don't have easy access to the OSG, but I have certainly tried and did manage to dig up an "Electricians guide to the IET" (17th ed though), and I really appreciate the effort everyone is making to help. As I understand it, this type of socket is aimed at use where the equipment used on the ring can collectively (if not individually where they would need wiring in) generate a high protective current (mainly office buildings) and the sockets being installed must have 2 earth terminals. These terminals each link to one end of the ring, and to each other and a duplicate earth or metal conduit (to ensure the earth is protected in case of a component/socket failure). As such I guess the verdict is that the sockets are likely to pass BS 1363/Plug and socket regs, and be legal to sell, but the installer will be responsible to ensure safe fitting. That means to bridge the two terminals with a suitable conductor and run duplicate conductor/metal trunking in in the office setting. In the domestic setting an installer would just bridge the two earth terminals (unless the householder was going to have a host of PCs installed and needed duplicate earth wire/trunking) - In the DIY arena the bridging of terminals is unlikely to happen all the time, and would depend on the user's level of ability and desire to read the instructions, but remains legal-but-iffy to use. Does that sound about right?Have you bothered to read the OSG details I provided?
I rarely post because there are so many adverts on here I can’t be bothered most of the time to have to put up with the barrage, and I don’t like the cookie policy. As I understand it it requires you to allow too much cross site tracking and persistent cookies. I don’t believe that they are essential.where you bin hiding? long time no see. ?
Hassle on mobile devices though and I've not been at a computer so much recently.i use adblock. the only ads i see are the forum sponsorson the right side of my screen.
Hassle on mobile devices though and I've not been at a computer so much recently.
Plus I have enough in having to know the details of half a dozen pieces of law, keep up with the changes in these and the several hundred standards that are linked to the product safety legislation without getting involved with any legislation and standards outside this, so I don’t like that the forum has ”gone international”, can’t be bothered to find out the location of the poster, and thus the requirements of the law and standards behind the question. Just too much hassle.
Or me? Launch my channel with it?
I'll be in touch with electrical safety first shortly.
If you want it.Or me? Launch my channel with it?
Message me your address and I’ll get it sent tomorrow. Hermes or Post Office?Go on then. I promise not to set it on fire* or subject it to gratuitous violence.
*with petrol, although if it catches fire with electricity, that is its own lookout.
The law is not as specific as to give the level of detail you seek.So it is legal to have two separate unlinked earth terminals in a socket? BS 1363-2 doesn't seem to specify there must be a single termination, but it doesn't seem right to me as you could end up wiring one side of the loop into each termination, and split the earth loop by accident. either that or you end up with an unearthed socket. (or have to fit a link between the two. ) but is it legal? that's the question!
Electrical Safety First.So you all have a choice now, JW or Big Clive?
That's the trouble I have. It seems to comply with the standard (so long as the instructions are good enough to meet the lab's interpretation of the cl4 requirement "minimizes the risk of danger to the user or the surroundings") but I don't know the law/regulations well enough to say if this would fall illegal under the EHSRs on its own. I can check the LVD, but don't know if there is anything similar in the Part P or or other regs that would forbid this arrangement. [edit: sorry, you do clearly state the EHSRs require the product to be safe - - if there any laws other than the LVD/LV Safety Regs/plug and socket regs, could you point me to them please?)The law is not as specific as to give the level of detail you seek.
The EHSR’s of the law merely require the product to be safe.
A BS is not law and is not mandatory.
However deviations from a BS would mean that the manufacturers would have to be able to justify the same or greater safety than afforded by following the relevant BS product standards.
(much simplified explanation)
That's the trouble I have. It seems to comply with the standard (so long as the instructions are good enough to meet the lab's interpretation of the cl4 requirement "minimizes the risk of danger to the user or the surroundings") but I don't know the law/regulations well enough to say if this would fall illegal under the EHSRs on its own. I can check the LVD, but don't know if there is anything similar in the Part P or or other regs that would forbid this arrangement.
Plugs and sockets outlets are excluded from the LVD, because the standards to which they are made are national, not harmonised. I am not sure (but we should probably find out) how the LVD applies to a socket outlet with integral electronics, such that the electronics lie within the scope of the LVD. There is this: Announcement: server inaccessibility - European Commission - http://ec.europa.eu/DocsRoom/documents/20341 but I can't access it at the moment because the Europa site is down. It might only concern plug-in devices, I can't recall.
Part P doesn't care a jot how the terminals on a socket outlet are arranged. It is a building regulation that obliges installers to comply with BS7671 in order to also comply with building regs, and to notify and certify certain works. It does not apply at all in many locations. BS7671 does not itself explicitly require socket outlets to be made to BS1363, however any alternative would be expected to achieve the same level of safety and it would be an uphill struggle to demonstrate how a socket not made in compliance with that standard would do so, in a UK domestic environment.
Who has a copy (or sight of a copy) of BS1363?
With my regulatory hat on ........
The UK 'law' on plugs and sockets is implemented through Statutory Instrument 1768, "The Plugs and Sockets etc. (Safety) Regulations"
This specifically requires socket outlets to comply with BS1363-2 plus amendments.The Plugs and Sockets etc. (Safety) Regulations 1994
These Regulations re–enact with modifications the provisions of the Plugs and Sockets etc. (Safety) Regulations 1987 (S.I. 1987/603) and make provision for the first time for certain requirements to be satisfied in relation to appliances.www.legislation.gov.uk
The standard defines not only construction requirements but also the plethora of tests that must pass for the design to be approved.
It requires products to be tested and approved (type testing) by an accredited test house, to the standard, before they are put on the market, and requires marking on the product to identify the test house to show compliance.
It is not permitted to CE mark plugs and sockets (now going to be UKCA since Brexit), 'self declaration' is not allowed for plugs and sockets, so the only legitimate route to market is through notified body testing.
The Socket under discussion has a spurious CE mark. I didn't see the mark of an accredited test house anywhere, and as Lucien commented on the 'instructions', I don't think any test house would have passed the instruction leaflet anyway.
I don't believe there is anything specific in BS1363-2 to say that multiple earth terminals must be connected (I could be wrong), so that doesn't help the cause, but it is plain that supplying these things is against regulations, so I believe Trading Standards could take action.
As I understand it only Standard Plugs need Notified body approval (Regulation 8) but Sockets fall under "Regulation 10 Electrical devices other than standard plugs" which only require testing. Agreed re: BS 1363-2, though, I can't find anything specific in that states that the earths must be linked, but the General requirement in cl.4 states that risks must be minimised so it is down to the lab interpretation of what this means. CE would still be needed if there is a CE Function like WiFi under Radio Equipment Directive/Regulations.With my regulatory hat on ........
The UK 'law' on plugs and sockets is implemented through Statutory Instrument 1768, "The Plugs and Sockets etc. (Safety) Regulations"
This specifically requires socket outlets to comply with BS1363-2 plus amendments.The Plugs and Sockets etc. (Safety) Regulations 1994
These Regulations re–enact with modifications the provisions of the Plugs and Sockets etc. (Safety) Regulations 1987 (S.I. 1987/603) and make provision for the first time for certain requirements to be satisfied in relation to appliances.www.legislation.gov.uk
The standard defines not only construction requirements but also the plethora of tests that must pass for the design to be approved.
It requires products to be tested and approved (type testing) by an accredited test house, to the standard, before they are put on the market, and requires marking on the product to identify the test house to show compliance.
It is not permitted to CE mark plugs and sockets (now going to be UKCA since Brexit), 'self declaration' is not allowed for plugs and sockets, so the only legitimate route to market is through notified body testing.
The Socket under discussion has a spurious CE mark. I didn't see the mark of an accredited test house anywhere, and as Lucien commented on the 'instructions', I don't think any test house would have passed the instruction leaflet anyway.
I don't believe there is anything specific in BS1363-2 to say that multiple earth terminals must be connected (I could be wrong), so that doesn't help the cause, but it is plain that supplying these things is against regulations, so I believe Trading Standards could take action.
You are right, and Schedule 1 actually excludes sockets that incorporate another electrical device (eg usb or Wi-Fi). Must learn to read thoroughly!As I understand it only Standard Plugs need Notified body approval (Regulation 8) but Sockets fall under "Regulation 10 Electrical devices other than standard plugs" which only require testing. Agreed re: BS 1363-2, though, I can't find anything specific in that states that the earths must be linked, but the General requirement in cl.4 states that risks must be minimised so it is down to the lab interpretation of what this means. CE would still be needed if there is a CE Function like WiFi under Radio Equipment Directive/Regulations.
Also note in the MK instructions:I believe someone has mentioned "clean earth" sockets where the terminals are not linked, MK produce one but the terminals are marked different as can be seen here. I doubt however the accessory we are discussing has been designed for this purpose.
The issue I have with PSSR is that whilst it states "sockets" and includes sockets in regulation 3 "Interpretation", includes them in reg 4 "Electrical devices to which Part I applies", and goes on in para 6 "Requirements for electrical devices" therein it specified compliance for plugs to contain a BS 1362 fuse (in 6(2)) and in 6(1) requires compliance with reg's 8 or 10, these go on to not specify sockets!With my regulatory hat on ........
The UK 'law' on plugs and sockets is implemented through Statutory Instrument 1768, "The Plugs and Sockets etc. (Safety) Regulations"
This specifically requires socket outlets to comply with BS1363-2 plus amendments.The Plugs and Sockets etc. (Safety) Regulations 1994
These Regulations re–enact with modifications the provisions of the Plugs and Sockets etc. (Safety) Regulations 1987 (S.I. 1987/603) and make provision for the first time for certain requirements to be satisfied in relation to appliances.www.legislation.gov.uk
The standard defines not only construction requirements but also the plethora of tests that must pass for the design to be approved.
It requires products to be tested and approved (type testing) by an accredited test house, to the standard, before they are put on the market, and requires marking on the product to identify the test house to show compliance.
It is not permitted to CE mark plugs and sockets (now going to be UKCA since Brexit), 'self declaration' is not allowed for plugs and sockets, so the only legitimate route to market is through notified body testing.
The Socket under discussion has a spurious CE mark. I didn't see the mark of an accredited test house anywhere, and as Lucien commented on the 'instructions', I don't think any test house would have passed the instruction leaflet anyway.
I don't believe there is anything specific in BS1363-2 to say that multiple earth terminals must be connected (I could be wrong), so that doesn't help the cause, but it is plain that supplying these things is against regulations, so I believe Trading Standards could take action.
BS 1363-2The maximum load from a 2G 13A socket is usually taken as 20A. Where does this figure come from? Written into legislation somewhere, manufacturer's instructions or just a convention?
That is in BS 1363-2, "16 temperature Rise" 16.1.2 for fixed sockets, using Table 10. "loading of sockets for temperature rise test". - 2 outlets are loaded with 1*14A+1*6A, total nom. load on supply cable 20A.The maximum load from a 2G 13A socket is usually taken as 20A. Where does this figure come from? Written into legislation somewhere, manufacturer's instructions or just a convention?
Bring back ductor testing?...What we might have to rely on is the inadequate instructions. They mention a single earth wire, which cannot reasonably be understood as a wire to one terminal and a link to the other. Nor would a person skilled and qualified in electrical installation work be expected to know that a link is needed. Whilst such a person would test the completed work, which would reveal the issue in many cases, an end-of-radial tested at whichever socket has the CPC connected would show nothing abnormal. Even in RFC or middle of a radial, a fortuitous connection between the two terminals via the screws and back-box could yield satisfactory test results without the connection being adequately reliable.