i fancy paying it off the roll and then when its short i will get wholesaler to coil it back up and grovel to me for selling me less than i asked for!! if it is 100m then i donald ducked and will have a snotty pile of cable!!
Ha ha that i would love to see!! you with a massive pile of payed out cable all over your drive!!
Don't confuse length of ring with max floor area, I think the max length limited by volt drop is around 127M allowing design current of 20A
I said you explination of the formula was correct but where do you get your numbers from??
4 x 11.5 x1000 is correct but your Ib will not always be the max admissible current allowed but in a ring that is correct. however i cannot check your mV/a/m as i dont have the regs to hand.
volt drop for 2.5 is 18, using the mcb of 32a as Ib. kitchen ring main has got me thinking in a barn conversion, due to the above size rooms to a standard house. It is measuring out at about 53 metres, just applying the maths to it and getting my head around it