So can someone help on this scenario.

Plant room prob 7Mx7M square ish. Loads of HVAC, pumps etc as you would expect and a ring final circuit.

Socket been damaged somehow and went to replace socket.

After replacing socket just for peace of mind we test that circuit. IR ok elip ok polarity etc.

Test RCBO and with cables disconnected as per GN3 all ok.

Just testing further and left loop tester on high current and the RCBO did not trip unusual so we got out RCD tester and couldn't get the RCBO to trip from socket. Yet with cables disconnected works as should.

So what going on and ae replaced RCBO and same ?

But circuit looks ok all in tact all tests on circuit as expected.

So unplug everything thinking maybe some item plugged in causeing problem but NO joy still.

Anyone ?
 
Might seem daft but are you sure the socket is fed from that rcbo?

Also as mentioned above, possible dc locking of the coil due to inverters or other equipment in plant room passing dc into mains.
 
Definitely correct circuit and confirm the ring is complete and figure 8 test all good.

All in right place all through circuit L,E and N.

The dc from other stuff good shout so ill try turning off other stuff see if makes a difference.

Its all sockets on that circuit we even tried testing at the Type B rcbo 32A direct on terminals cables connected wont trip but connected out of RCBO and operates as should.

Now also question was would people class this as a defect as to gn3 i done tests correctly its only further testing thrown this issue up ?
 
HAve you tried reversing the phase of the test current ie using the 0 and 180 deg positions?

And measure the N-E voltage at the RCBO output and socket. Most RCD testers do a pre-check of voltages and also check that the E/cpc will not rise above 50V when the test current is injected.

Is it a single or double pole RCBO?
 
Last edited:
Check N-E IR of the ring at the RCBO but disconnected from it with all socket switches in the on position and all loads unplugged.

Check ring continuity and compare readings of L-L N-N and E-E.

Does the ring supply equipment which is equipotential bonded to MET?

What is earthing system please?

What happened to cause damage to the socket and what was the effect of the damage?
 

Reply to Lets see how good this forum is ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
948
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top