L

llywelyn111

A sparky that I know very well and is a good sparky (went to college with him) just rang me up. He has a fault on a lighting in a log cabin. He says he's IR'd the circuit that blows the MCB and RCD and is totally clear. He said a two gang dimmer, one of them doesn't dim now. So I said it must of being the dimmer failing causing a short. He changed the dimmer MCB back on Customer made him a coffee. 15 mins later MCB and RCD trips again. Same dimmer blow again and now won't dim again.

400watt dimmer with x4 50watt GU10 on that dimmer.

Told him to IR it again and it's totally clear (lamps taken out).

Told him to leave the light on with the blown dimmer so it would just work like a normal switch. Still blows after about 15-45 mins.

so it's got to be that switch live and neutral T&E (feeds taken to switch, no access above due to vaulted roof) from that dimmer that has been damaged somehow. Anything else I could get him to check? or come across something like this before.
 
put normal switch on and try again. if still blows, isolate out-going side of switch and try again, at least u find which side causing problems. could be heat from lamps cooking trapped cable or rodent damage?
ive had water in t&e cables and when it gets hot the IR drops. dont know why but it does.
i hate halogen spots.
best of luck.
 
It's a new log cabin, so can't be rodent damage. He says it still trips only with them four lights connected in a temp 1 gang switch. So it must be a trapped cable or coving pinned and damaged the cable. He'll have fun replacing the cable haha
 
just the thing for sunny sunday afternoon eh?
i'd be looking at the connections to the lamp holders first and then a good pub second (you know, one with no mobile signal).
 
when he did IR between live conductors and earth, he didnt disconnect the cpc in the cable from earth did he? so it might apear clear
 

Reply to Light circuit fault in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
224
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
791
The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top