Hi,

I have a lighting circuit which trips the RCD, I’ve got pared back so that if I take one brand new light fitting and wire it directly into the consumer unit with a brand new cable - and still the RCD trips. If I remove that wire from the consumer unit and put a 3 pin plug on it, and plug that 3 pin into the mains rings, one sockets ring works fine and the other trips out.

The lighting ring is a 6A MCB and the socket ring that also trips out is a 32A MCB, both on the same RCD; the socket ring that does not trip out is also 32A, but protected a separate RCD in the same CU.

The CU was brand new a few months ago (not fitted by me, it’s a properly certified installation) and came fully populated. Total current draw at the main fuse is around 2A so the MCBs are definitely not overloaded.

How is this possible? Dodgy RCD?

Thanks
John
 
Hi,

I have a lighting circuit which trips the RCD, I’ve got pared back so that if I take one brand new light fitting and wire it directly into the consumer unit with a brand new cable - and still the RCD trips. If I remove that wire from the consumer unit and put a 3 pin plug on it, and plug that 3 pin into the mains rings, one sockets ring works fine and the other trips out.

The lighting ring is a 6A MCB and the socket ring that also trips out is a 32A MCB, both on the same RCD; the socket ring that does not trip out is also 32A, but protected a separate RCD in the same CU.

The CU was brand new a few months ago (not fitted by me, it’s a properly certified installation) and came fully populated. Total current draw at the main fuse is around 2A so the MCBs are definitely not overloaded.

How is this possible? Dodgy RCD?

Thanks
John
Borrowed Neutral,
 
The CU was brand new a few months ago (not fitted by me, it’s a properly certified installation) and came fully populated.
If I remove that wire from the consumer unit and put a 3 pin plug on it, and plug that 3 pin into the mains rings, one sockets ring works fine and the other trips out
I take one brand new light fitting and wire it directly into the consumer unit with a brand new cable - and still the RCD trips.
and you have wired it your self ?either you have a borrowed Neutral or its been wired up wrong .
 
From the description of what you have tried I cant see how it could be a borrowed neutral. You need to do an RCD test on both RCDs and also an insulation resistance test on the light fitting, and potentially a leakage test on the side that trips. It does sound like a faulty fitting and potentially faulty RCD. But it could also be that the side that is tripping has a high background leakage and that fitting is just tipping it over the edge. Is it some kind of LED fitting?
 

Reply to Light fitting trips one RCD, but not if connected to a different RCD in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
488
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
939
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
450

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top