Hi guys, was asked to have a look at a lightng circuit in a local house but it has baffled me. the mcb hasnt tripped and neither has the rcd. no changes to fittings etc. out of the whole house 2 lights still work and the rest dont. teting the voltage at a few of the light fittings. im getting 240 between earth and live but earth and neutral only 24v? didnt have time to do continuity on circuit etc as was only a quick call as going out. just wondered if any1 gotideas of what it can be? any help appriciated, cheers.
 
Will do that, thanks, just upon quick check consumer unit under stairs, kitchen next to it ok. lounge next to that ok then from there on it doesnt work. as stated, i had 240 earth to live but only 24 neutral to live. so it would be a loose neutral?
 
broken or loose neutral in a ceiling rose ( assuming loop in at lights ). could be a break in a conductor, but unlikely. hopefully you've not got JBs under the floor all over the place.
 
i had the same problem mate, it turned out to be a loose neutral in a connector block behind a switch. There were 4 neut's going into the block but one was wedged in between the copper terminal and the plastic housing. it had been fine for 3 years and slowly came loose. Also seen afew neutral faults at ceiling rose...over tightened and snapped or simular.
 

Reply to lighting circuit fault in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
344
  • Question
This is a baffling fault I've been fighting with for a couple of weeks now, so I wondered if another set of eyes will help. I installed an EV...
Replies
0
Views
186

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top