Hi,

Quick question. If the consumer unit is located near the middle of area to be served by the lighting circuit, is it allowable to run the circuit as two radials from the same RCBO, one running in each direction?

Thanks,

Tony S
 
Re: Lighting circuit - is it allowable to have two branches from the distribution boa

Yes, nothing wrong with this at all.
 
Re: Lighting circuit - is it allowable to have two branches from the distribution boa

As long as the over-current rating of the RCBO is appropriate for the smallest cable size connected to it I also wouldn't see a problem.
 
Re: Lighting circuit - is it allowable to have two branches from the distribution boa

Just remember that this is still one circuit, not 'two radials'. It also means you have to test two 'ends' for EFLI and go with the highest.
 
Re: Lighting circuit - is it allowable to have two branches from the distribution boa

Thanks for quick and clear answers. EFLI won't be a problem as even the total length of cable will be less than if I had to wire as one leg, and as you say the limit will be the longest leg rather than the total of the two.

Strictly, would this be considered a radial circuit with a spur, with the spur just happening to come from the CU?

My only original concern was that it was a slightly odd layout. If I was using MCBs I'd probably just make it two circuits for clarity, but it's RCBOs so don't want to splash out unnecessarily.
 
Re: Lighting circuit - is it allowable to have two branches from the distribution boa

classes as a radial circuit of 2 branches. a spur only applies if off a RFC.
 
Re: Lighting circuit - is it allowable to have two branches from the distribution boa

Thanks, that makes sense.
 

Reply to Lighting circuit - is it allowable to have two branches from the distribution board in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Written in clauses are essential, but should be fairly standard fare to a solicitor. A similar situation exists around where I live with regard to...
Replies
9
Views
586
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top