Lighting Circuit.. Surely This Isn’t Right? | Page 3 | on ElectriciansForums
Discuss Lighting Circuit.. Surely This Isn’t Right? in the Lighting Forum area at ElectriciansForums.net
You are forgetting that you are working it out at 12 volts, if you transpose it to 240 volts (for ease of calculation then divide your 4.2 amps by 20 which comes to 0.21 amp, so 5 LV lights to 1 ampish, so why not put 20 or so lights on a circuit, calcs work out alright.
Don't forget to add in the power factor load of the transformers ;)
On a serious note, all these quotations of loads on the 1.0 don't mention that the cable should be de-rated as, being a lighting cable, it will undoubtedly be going through loft insulation, bunched with other cables, and goodness knows what else on its route, knocking the CCC down considerably. I know 'official' cable calcs often give ridiculously pessimistic results, like demanding a 10mm cable for a lighting circuit because of all the factors, but in this case 1.0 really doesn't seem enough.
It would be be interesting to do a proper calc with the given load, and all the insulation, grouping, and other factors, and real length and see what it comes up with.
and did any one mention diversity..... ive pushed circuits to limits .... forget future proofing...... will keep us in work and are quotes will be slightly cheaper
You can probably count the amount of times ALL of a circuits lights are on, within a domestic setting on one hand over the lifetime of the installation!! As far as i'm aware, 100W incandescent lamps are no longer available, and 60W lamps are soon to follow.
I'm not saying that the circuit as described by the OP is a particularly good one, but most are over assessing the actual demand load that this circuit will ever see!! Diversity is a wonderful thing, to those that know how to use it!!! lol!!
Oops didn't read the date! It was on the front page so I thought it was quite recent. Never mind, that house has probably burnt down by now, from a 1.0 cable melting onto some newspaper in the loft!
Yes it is. I've never liked the idea of diversity on lights. In houses inhabited by rich and/or lazy people it is common to have all lights blazing all day and most of the night whether anyone's in the house or not. In my two-room hovel it is very common to have both candles alight at once, so no diversity here...
haha!! Are you saying that it's common for householders to have every lamp switched on a circuit, including exterior lighting?? I don't know what world your living in but it's not mine. Diversity ''always'' needs to be applied, especially in domestic installations, or you'll be asking the DNO for a cut out fuse of around 160+A.
Reply to Lighting Circuit.. Surely This Isn’t Right? in the Lighting Forum area at ElectriciansForums.net
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
Also posted in DIY. strange one in my kitchen. 3 sets of 2-way switched mains GU10 Philips down lighters. ( no dimmers) Have been fine for...
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...