Lighting circuit with 2A & 5A sockets | on ElectriciansForums

Discuss Lighting circuit with 2A & 5A sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

O

Octopus

So, 1970 ish flat, 16ed board fitted in 2007, MCB covering lighting circuit. Lighting circuit has 4 x 2A/5A sockets on it.

Should they be covered by RCD/RCBO?

My feeling is no and code it C3, with a recommendation to upgrade MCB to RCBO?


Thoughts please chaps.
 
I would have thought no as it was done in line with the regulations at that time. I take it it's not tt and its only lighting plugs that can fit in the sockets?
 
I would have thought no as it was done in line with the regulations at that time. I take it it's not tt and its only lighting plugs that can fit in the sockets?

It is only 2A or 5A plugs that fit in the sockets, which in a domestic environment will only be lighting. In other environments it could be any number of things on such plugs, not just lighting.
 
Yes they should be....411.3.3. But if they complied at the time of installation and are not likely to supply equipment outdoors....(clearly not) then code 3.
If you lablel them as specifically for table lamps then no code at all IMO 411.3.3 (b)

Recently I got called out to a similar install with 13a sockets instead of 2/5a's. During a dinner party they'd plugged in a 2kw fan heater....untill someone noticed the dimmer switch was on fire!
 
Usually on the either/or type codes I look at the rest of it as a whole, if it is all spot on other than being to the earlier edition I tend to be a bit more generous and code more leniently, OTHO hand if it is a pile of poo with other C2s then I code more harshly.
 
I would code the lack of RCD additional protection for the sockets as C3. I have only ever once issued a C2 for this issue in fact.
However if there is a 13A outlet in place of a 5A outlet (I think this is the case here) on this lighting circuit, then it must be a C2 surely due to the lack of co-ordination between potential current draw and rating of accessories such as light switches. The dangers are pointed out ably by wirepuller's example in post #5.
 
I would code the lack of RCD additional protection for the sockets as C3. I have only ever once issued a C2 for this issue in fact.
However if there is a 13A outlet in place of a 5A outlet (I think this is the case here) on this lighting circuit, then it must be a C2 surely due to the lack of co-ordination between potential current draw and rating of accessories such as light switches. The dangers are pointed out ably by wirepuller's example in post #5.

Yup - I didn't really mention that on the EICR as the client commented about a problem and wanted it fixing!
 
Seriously ? If having a socket which only the lamps can be plugged in to and is controlled by a lightswitch isn't enough what the hell difference is a label going to make?

Sorry, silly assumption really. I still stand by my point though that are not general use sockets and being a completely different size and shape plug counts as being restricted to a specific load.

I understand where you are coming from but the question is about codeing for lack of RCD protection to a socket outlet. I'll refer you to the reg I quoted which makes no distinction on socket type....only that the rating is 20a or less. Which means that in order not to code a 2/5a socket must either have rcd protection,or be specifically labelled. You are assuming that DIY dave will know that a 2/5a socket is only for a table lamp,thats an assumption too far.
 

Reply to Lighting circuit with 2A & 5A sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top