OP
R G
IMO , these sockets still supply hand held or portable equipment so should be RCD protected , regardless of previous regs..........
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Lighting circuit with 2A & 5A sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I did notice this "neat" bit of earth sleeving on the shaver point.
View attachment 28083
Yup its normal to use green and yellow but a bit of blue and a bit of brown!!
At least it complies with the ratio of colours for a bi-coloured protective conductor! :smilielol5::mickey::cowboy:
I understand where you are coming from but the question is about codeing for lack of RCD protection to a socket outlet. I'll refer you to the reg I quoted which makes no distinction on socket type....only that the rating is 20a or less. Which means that in order not to code a 2/5a socket must either have rcd protection,or be specifically labelled. You are assuming that DIY dave will know that a 2/5a socket is only for a table lamp,thats an assumption too far.
I see your point but its all open to interpretation!
Note b of the reg you have quoted (411.3.3) states that the socket does not have to be RCD protected if its 'provided for connection of a particular item of equipment' - which the 2A/5A plug does, to my mind.
Obviously some muppet could change a 13A socket to a 2/5A socket but anyone with a screwdriver can do want he wants. All I say is let them suffer the consequences!
There's nothing to stop a 2/5a plug being put on any other item of equipment though. you cant assume that such a plug will only be used on a table light,there are plenty of people who would be daft enough to stick a 5a plug on their hair dryer if that was the most convenient socket!
You'd just love to have seen that.Yes they should be....411.3.3. But if they complied at the time of installation and are not likely to supply equipment outdoors....(clearly not) then code 3.
If you lablel them as specifically for table lamps then no code at all IMO 411.3.3 (b)
Recently I got called out to a similar install with 13a sockets instead of 2/5a's. During a dinner party they'd plugged in a 2kw fan heater....untill someone noticed the dimmer switch was on fire!
No code for me, this coding has become total bolloxSo, 1970 ish flat, 16ed board fitted in 2007, MCB covering lighting circuit. Lighting circuit has 4 x 2A/5A sockets on it.
Should they be covered by RCD/RCBO?
My feeling is no and code it C3, with a recommendation to upgrade MCB to RCBO?
Thoughts please chaps.
No code for me, this coding has become total bollox
Reply to Lighting circuit with 2A & 5A sockets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net