S

Spannaz

Hi Guys,

Just been to do a Condition report on a 30 year old installation. Both lighting circuits are wired in twin stranded steel cable with no CPC. The insulation test is good, but with the lack of CPC, and brass accessories, would you consider this as 'Satisfactory'. No RCD on lighting circuits either.
 
Steel cable? Rcd on light circuit to the bathroom? Is there metal conduit acting as cpc?

Nope, nothing acting as CPC. I did the report yesterday and failed it, customer rang this morning and tore strips off me as she's had someone else in and they've passed it. The other big issue is that the Insulation Resistance on the ringmain Line to CPC was 3.4M. OK, just scrapes through...but not good. How can someone pass it. They told her just to use plastic light switches and she'll be alright LOL There is even brass wall lights. I mean....really?!?!?!?!?!?
 
Nope, nothing acting as CPC. I did the report yesterday and failed it, customer rang this morning and tore strips off me as she's had someone else in and they've passed it. The other big issue is that the Insulation Resistance on the ringmain Line to CPC was 3.4M. OK, just scrapes through...but not good. How can someone pass it. They told her just to use plastic light switches and she'll be alright LOL There is even brass wall lights. I mean....really?!?!?!?!?!?

Stick to your first report mate. She may not like it but its your neck on the line.
 
all accessories would need to be class 2 (including switches) for a c3 and warning label attached to cu, anything other would be a unsat report.

were you paid? what was the reason for the report?

thought no cpc dated back to early 60s around 50year ago.
 
more than 30 years old. more like 40 - 50. with stranded cable, tinned or otherwise.
 

Reply to Lighting circuit with no CPC, fail??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
856
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top