So if a circuit is really overloaded but has the correct mcb then you don't mention it on EICR ?

No you don't because it's not overloaded. The cable is adequate for the circuit and the OCPD is adequate for protection of the cable.

You should only be issuing a code to an observation on an EICR if it breaches a reg and you can reference that reg.
 
Yet again, I'm caused to call the competence of someone into question, when in fact by very requirement of quals such as 2391, anyone engaging in Inspection and Testing would be expected to have above average experience and knowledge.

Please, someone tell me that it's not just me thinking this, surely??!
 
Deleted.
 

Reply to the thread, titled "Lighting circuits query" which is posted in Periodic Inspection Reporting & Certification on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Lighting circuits query
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
krr4,
Last reply from
davesparks,
Replies
19
Views
2,332

Advert

Back
Top