A

akcorbin

Evening,

basically I have 3 lighting circuits controlled by a one photocell.

I have fed my photocell and then the switched live from the photocell comes down to my contactor.

My contactor is as follows


1. 3. 5.
A1

A2
2. 4. 6

I have taken the switched live from photocell to a1 and the neutral from photocell to a2.
I have taken my 3 lighting feeds to 2, 4 and 6
I have linked 1,3 and 5 to a1
i have connector blocked my 3 lighting feed neutrals and linked with a2

Please could someone tell me if this is correct?

Many thanks
 
No in a word.
From the way you describe it it seems that you are using the contactor as a glorified connector block.
The point of the contactor would be to switch live in and live out and or neutrals without running the power through the photocell.
Have you got lighting feeds and supplies or are you only feeding the lights from the contactor?

EDIT: It will, work however it seems a little pointless.
 
Last edited by a moderator:
Evening,

basically I have 3 lighting circuits controlled by a one photocell.

I have fed my photocell and then the switched live from the photocell comes down to my contactor.

My contactor is as follows


1. 3. 5.
A1

A2
2. 4. 6

I have taken the switched live from photocell to a1 and the neutral from photocell to a2.
I have taken my 3 lighting feeds to 2, 4 and 6
I have linked 1,3 and 5 to a1
i have connector blocked my 3 lighting feed neutrals and linked with a2

Please could someone tell me if this is correct?

Many thanks

You have no idea what you are doing,

And you should not be doing it!

Get an electrician to do the job for you.

It will be safer for you.
 
Your contactor looks to me to be single pole, would be better being double pole so as to isolate the neutrals as well as the lives.
The switchwire from the photocell needs to go into a1 alone. On your contactor 1,3,5 will have the 3 feeds from the fuseboard or 1 feed linked to 3,5. Connections 2,4,6 should be the switchwires as it were to the 3 lighting circuits. So once the photocell activates it pulls in the coil A1 and energizes all the lighting circuits, the neutrals will have to go in a connector block or din rail, A2 needs a neutral to work the coil.
 
So no point to having the contactor then.
I think Moses makes a good point.
However, very quickly, 3 x times lighting supplies from main board lives through contactor 1 3 5. Lives out to lights from 2 4 6. Join neutrals together seperately.
Feed live and neutral to photocell then switched live and neutral to A1 (switched live) and A2 (neutral).
Good luck but I would seriously take note of what Moses says and get a professional in.
 
Here's how I'd wire it...


[ElectriciansForums.net] Lighting contactor


***EDIT***

Just noticed the missing neutral to A2. Just take one from neutral bar
 

Reply to Lighting contactor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
Replies
8
Views
508
You only need to switch the lines and the contactor is rated per pole so for example a 16A four pole contactor would be fine.
Replies
1
Views
276

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top