Has it been raining down their sounds like water in an outside light , firstley remove all the light bulbs on the circuit and do a continuity test to ensure that the cpc are continuous through out the lighting circuit in question ,remove L and N from the board and do a continuity test between the L and the CPC then again N and the cpc then just do a continuity test across the L and N unless there are Pirs or external PIR lights outside these should give no reading then carry out the same tests using the Insualtion tester first test at 250 volts just in case there is something in circuit then increase the voltage to 500 and repeat the tests , i sound like a low insulation fault oh you will have to operate all the light switches during the tests to ensure the cables are ok , othere possible faults are burn out wirng in a pendant , rodent attack with rodent attached to cables causing a low insulation short fault low energy lamp