Hi all. Just wanted to resurrect this one as I've found something in the regs that would mean a 13A BS1362 fuse may not be appropriate for protecting lighting in many cases, and wouldn't have been suitable in this instance. It's to do with the co-ordination between conductor and overload protective device.

433.1.1
The operating characteristics of a device protecting a conductor against overload shall satisfy the following conditions:
...
(iii) the current (I2) causing effective operation of the protective device does not exceed 1.45 times the lowest of the current-carrying capacities (Iz) of any of the conductors of the circuit.

For a 13A BS1362, it appears I2 is 26A.

26/1.45 = 17.9A

So for 1mm² T+E, the 13A fuse would not comply in any case, and for 1.5mm², it would only comply if ref. method C.

View attachment 57198
A single light or lights wouldn’t necessarily require overload protection by nature of the load fed from a fused spur
 
Hmm. There's certainly a few sides to this. I must admit on the odd occasion I've been in situtions like this (for example in my own under stairs cupboard) I have taken a 13a FCU from adjacent RFC > 2x Sockets > 5a SWFCU acting as the light switch itself.

I think for me, in that instance it just acted as 'neat' way of changing conductor sizes down to the 1mm I used for the light. And just because it seemed logical. The source FCU was some distance away, it may "look wrong" if someone were to see a light fitting coming straight off the back of a socket (albeit fused 13a at the source FCU). The FCU for me acted more as a light switch and differentiation point.
 
I just think it's always good practice for the OCPD to be rated lower than the ccc of the circuit cable,regardless of the 'fixed load' and it's no bother in a loft /outbuilding or similar to fit a sfcu instead of just a normal light switch. Always done it this way and I see no reason to change now.
 
Where did you find the current/time plot for the BS1362 fuses? I have not seen that in any (obvious) place the few times I looked.
Maximum Zs for a 13 amp bs1362 fuse is 2.30 ohms 0.4 disconnection time , table 41.2
For a 5 second disconnection time it is 3.64 ohms table 41.4
Or 13 x 1.45= 18.85 amps
[automerge]1587045045[/automerge]
Where did you find the current/time plot for the BS1362 fuses? I have not seen that in any (obvious) place the few times I looked.
Maybe try this [ElectriciansForums.net] Lighting from fused spurs
 
Last edited:
I just think it's always good practice for the OCPD to be rated lower than the ccc of the circuit cable,regardless of the 'fixed load' and it's no bother in a loft /outbuilding or similar to fit a sfcu instead of just a normal light switch. Always done it this way and I see no reason to change now.
Coz we are old school Dave.
 
Sometimes you need to simplify things I say. Is adding an FCU before a light switch make the situation dangerous. No? Does it break any regulations? No. Would it make sense to a future electrician? Sure, even if they don't agree with it. So therefore it's not worth worrying about IMO.
 
Sometimes you need to simplify things I say. Is adding an FCU before a light switch make the situation dangerous. No? Does it break any regulations? No. Would it make sense to a future electrician? Sure, even if they don't agree with it. So therefore it's not worth worrying about IMO.
Indeed, it is a very minor point. But I enjoy chatting carp about the minutiae of our trade
 
Indeed, it is a very minor point. But I enjoy chatting carp about the minutiae of our trade

Oh absoloutely (I can get into pretty boring in depth detail about 13a plugs!) I just felt it a point worth mentioning. I'm guilty of getting wrapped up in thought on a job and often find myself having to strip it back a bit when in a job situation.
 

Reply to Lighting from fused spurs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top