I've been scratching my head today on a survey and before I advise remedial work just want to be sure I'm not missing something obvious.. Firstly 3 strand 1.5, singles into the board with no CPC at the board, but all light fittings have a cpc and worst fitting R1 R2 was 0.6ohms so quite high. Seeing this I did IR test at the board got an odd result so checked any thing that may affect this. Isolated boiler at switch and two fans at fan iso, still rubbish, removed lamps still rubbish. Disconnected both lighting circuits and IR'd R1, MET and getting 0.03M R1,Rn .05M upstairs R1,Rn is dead short 27ohms. Is there anything else that would give this reading?Lamps I've missed, security lighting..etc The RCD main incomer isn't tripping??! If I sort it.. how do I write up missing CPC at board and what CSA do I fill in as I have seen everything from 0 to 2.5mm (none at DB, 1mm most fittings but found a 2.5 of a shower cable in another..) shall I just put a range! LOL