Are there any shaver sockets?

Don't fall into the trap of ticking the 'separation box' because you have a shaver socket on an installation, the regulations apply to a separated final circuit ie. where the separation is distributed.
 
Good point but no shaver socket. I think I will start by trying to find where the circuit enters the loft as it's fairly straightforward, split it and IR back at the board. Got to start somewhere...
 
I am sure I will be slapped for this and put right... but when I was testing today all my readings were the same for 250v as 500v so why is it important to test at 500, I know we test Selv LN/E at 250 or anything not sure about LN/E 250 but if we get the same readings 250/500 for singles, seems a good idea to go this route and not damage equipment, I accidentally IR'd the boiler yesterday as I wasn't expecting it on the lighting circuit, luckily on 250. Isn't it prudent to test the lot at 250 most of which may max >999M and if we get a low reading then check carefully before switching to 500 for confirmation?
 
if you think of the IR test as a 'pressure' test then the 500V test stresses the insulation more than the 250V test.

You can use the 250V setting as a 'pretest' if you like.

When insulation is deteriorating, you'll certainly see a difference in the reading between the 2 voltages.

Current is limited to avoid 'burning out' a fault and giving a false 'clear reading'.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Lighting IR low help....!
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
Just,
Last reply from
IQ Electrical,
Replies
18
Views
2,197

Advert

Back
Top