Lighting issue | on ElectriciansForums

Discuss Lighting issue in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jun 21, 2021
Messages
5
Reaction score
1
Location
Billericay
Has anyone come across this before, client told me all lights were working previous to fuse board change, but when I turn light on in one room to a fitting with lamp in, it trips out RCD, when lamp is removed and light switch is turned on and off RCD stays on, all other light fitting with lamps in on same circuit(4 in total)all work as they should, I have checked insulation resistance , there is 230v between live and neutral when switch on at the lamp holder , then 0v between live and neutral when switch is switched off. This has got me totally stumped, please help
 
Does just one RCD trip, or two?
If two RCDs trip, then expect a borrowed N - the circuit for the light in question, and the circuit the N is borrowed from.
if juts the one RCD trips, perhaps that light is wired across L and E, and thus tripping the RCD when operated. Could be mixed up connections in a ceiling rose, or elsewhere.
 
Does just one RCD trip, or two?
If two RCDs trip, then expect a borrowed N - the circuit for the light in question, and the circuit the N is borrowed from.
if juts the one RCD trips, perhaps that light is wired across L and E, and thus tripping the RCD when operated. Could be mixed up connections in a ceiling rose, or elsewhere.
JUST after A CU change I believe the OP said
 
JUST after A CU change I believe the OP said
Yes I noted that, not sure why you raise that? Before a CU change with no RCD, a L to E connection would not be noticed, after it would trip the RCD. And testing with no lamp in place, perhaps would not be noticed (or, of course, no testing!).
 
then the borrowed N is favorite. what you could have is a 2 way light with N from the upstairs lighting cct. and L from the downstairs. if up and down lights are on different RCDs then that would cause 1 or both RCDs to trip when the light is switched on with a load connected.
 
then the borrowed N is favorite. what you could have is a 2 way light with N from the upstairs lighting cct. and L from the downstairs. if up and down lights are on different RCDs then that would cause 1 or both RCDs to trip when the light is switched on with a load connected.
this is a 1 bed flat, with 4 rooms in total, only 1 lighting circuit, no 2 way lighting anywhere, all other lights can be on, and bedroom light switch can be on with no lamp in place, and all power stays on, as soon as you put a lamp in and switch light on, RCD trips
 
Could be that the fixing screws for the ceiling rose have penetrated one of the cables above the ceiling, creating a fault from neutral to earth, which would only cause the RCD to trip when the lamp is in and switched on.

Or somewhere else along the same part of the circuit.
 
Could be that the fixing screws for the ceiling rose have penetrated one of the cables above the ceiling, creating a fault from neutral to earth, which would only cause the RCD to trip when the lamp is in and switched on.

Or somewhere else along the same part of the circuit.
Will have a look, when I am next back at flat, thanks for all scenarios, hopefully one of them will fix fault
 
Had one similar on a board change, the outside light had been fed from the back door light switch. With no Neutral at the switch I was scratching my head as to where they had got a Neutral from.

Turns out they had fed a single down the partition wall and into a socket bellow to grab a Neutral.

Ended up disconnecting it and all was well.

This was from an up front RCD board to an all RCBO board and in this situation the only pre testing I do is an RCD test.
 

Reply to Lighting issue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Also posted in DIY. strange one in my kitchen. 3 sets of 2-way switched mains GU10 Philips down lighters. ( no dimmers) Have been fine for...
Replies
0
Views
213
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
430

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top