I’m on a phone mate, there’s no way I can follow that to see if it’s right on such a small screen. I wouldn’t mind someone posting some good feedback for you, seems to went to a lot of effort.
Got this on Monday so gave up the pints for the pencil and paper just trying to learn as much as possible 1 step at a time
 
And for your homework next week, we want the same configuration of lights and switches wired in;

a. 3 plate- loop in at light.

b. Neutral loop at switches.
 
I’ve not traced everything but it mostly looks ok. The only thing that jumps out as odd is the fan isolator and light in the toilet.

Your drawing has the perm live in going through the fan isolator to the light switch common in series, and there is no perm live feed to the fan. That arrangement means the light can’t come on with the fan isolator off.

Instead put perm live in directly to COM of the light switch and either parallel from that to the perm live of the fan isolator or run a separate perm live from the JB to the fan isolator and on to the fan (for a timed fan). You can then have the light on with the fan isolator off.
 
I’ve not traced everything but it mostly looks ok. The only thing that jumps out as odd is the fan isolator and light in the toilet.

Your drawing has the perm live in going through the fan isolator to the light switch common in series, and there is no perm live feed to the fan. That arrangement means the light can’t come on with the fan isolator off.

Instead put perm live in directly to COM of the light switch and either parallel from that to the perm live of the fan isolator or run a separate perm live from the JB to the fan isolator and on to the fan (for a timed fan). You can then have the light on with the fan isolator off.
Thanks a lot really appreciated like
 
On a more general note, even if you have all the connections correct, a drawing like that with conductors snaking around the page is of little practical use because it is slow and error-prone to follow. Think about what it is trying to communicate; for example that room 2 switch is fed from the main permanent line terminal, then sends its switched line to the light via terminal 9, then the neutral goes back to the main neutral terminal. The line and neutral connections are more or less the same for every room, a fact that is not obvious at all from the drawing. The only unique thing about room 2 here is that its SL is on terminal 9, which can be shown without miles of spaghetti.

Investigate different ways of simplifying the drawing without losing any information. Research the difference between a schematic circuit diagram, which shows what is connected together without being specific about which terminals the wires go into, and a wiring diagram that physically details each cable and connector.
 

Reply to lighting joint box in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
452
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
747
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Cheers guys. I was working on the same assumption, but was aware for MF the wagos in wago box were derated 32s, and couldn't find anything to...
Replies
7
Views
331
I
  • Article
weeping solvent weld joint Hi, I have a weeping solvent weld joint on my bathroom sink. What's the best way to seal it please? weeping solvent...
Replies
0
Views
137
Iankkk
I

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top