just been spammed with testing an installations Lightning protection system out in Afghan. was installed nearly a year agbo but the lad that installed it has now done one so i get the honour of testing it.
it has two sets of cabins each with 8 earth pits around them, the rods are not linked below ground, some of which are inaccessible now because of walkways etc.
i only have a fluke clamp meter as my megger is away for calibration so getting in to the pits to try & test is a no starter.
when i measure the down tapes i am getting the noise symbol on the test meter & when refered to the instructions makes the result void. this does not happen at every down tape only around half of them. the others pass but only just, around 9 ohms.
any ideas on how i could rectify the problem short of digging trenches & ensuring they get some sort of farraday cage type effect.
cheers.
it has two sets of cabins each with 8 earth pits around them, the rods are not linked below ground, some of which are inaccessible now because of walkways etc.
i only have a fluke clamp meter as my megger is away for calibration so getting in to the pits to try & test is a no starter.
when i measure the down tapes i am getting the noise symbol on the test meter & when refered to the instructions makes the result void. this does not happen at every down tape only around half of them. the others pass but only just, around 9 ohms.
any ideas on how i could rectify the problem short of digging trenches & ensuring they get some sort of farraday cage type effect.
cheers.