I have been called back to a job where a 3-halogen lamp fitting with 2 way switching keeps blowing a bulb. When this happens and the switch is turned off the remaining 2 lamps stay on but very dim. When the blown lamp is replaced, all is well again. I have tried everything. Isolated it from upstream lights, changed both double switches and tightened all terminals. Any ideas? Thanks.

Nick
 
sounds like a job i did not long ago!!

customer had new loft insulation fitted!!
installer disturbed a junction box and the live feed for intruder alarm came out!
been the nice installer he was he reinserted the red cable in to the red connector! (how ever he connected to the wrong red bit and actually connected to switch line from the landing light!

outcome!! when light on stairs is on it powers light and charges intruder alarm!
when light off it also disconnects alarm and the battery in alarm powers the light very dimly!

is your smoke doing the same!!! possibly the battery feeding the light!! i would double check the connections!!


may i also add the loft guy also mashed the screw terminals in JB!!! PRAT!!!!
 
Last edited by a moderator:
I fixed the problem in the end. I just fed the smoke into a jb on the same circuit just upstream and hey presto. Very strange, it deffo wasn't the switch wire I was feeding into! One of those mysteries.
Cheers All.
 

Reply to lights dim when turned off in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
667
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
345

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top