Hi all,

I’m having bit of a problem diagnosing a fault it’s already in my top 5 of hardest faults to find.
I’ll try to simplify lights on one circuit and also lamps plugged into sockets on the ring main sometimes flicker indicating it’s not just lighting circuit. My first hunch is loose connection in consumer unit rcd. Split load dual rcd however sockets and lights are on separate rcds. Next hunch the main switch is at fault however connections are tight and secure. It’s a terraced house with overhead supply apparently neighbours do not have same issue so can rule out loose connection on supply side HELP!!!
 
I'd be checking all connections in CU including bus bars, and neutral link wires first. Also N conductors for those two circuits.
Can you try moving the lamp to another circuit (e.g. cooker switch socket) and see if fault moves?
Have you checked supply voltage?
When did it start happening? Anything changed, e.g. have they just had a smart meter fitted?
How often does it happen, how long do you have to stand there to see it?
 
I'd be checking all connections in CU including bus bars, and neutral link wires first. Also N conductors for those two circuits.
Can you try moving the lamp to another circuit (e.g. cooker switch socket) and see if fault moves?
Have you checked supply voltage?
When did it start happening? Anything changed, e.g. have they just had a smart meter fitted?
How often does it happen, how long do you have to stand there to see it?
I’ve disconnected and reconnected everything in the consumer unit, I’ve checked the supply voltage whilst there reading 234v I didn’t believe the customer at first but I asked them to record the flickering which they did and the lights do flicker I’ve supplied them with LED lamps (bulbs) but it still does it. It’s all circuits (down ring)(up ring) have not tried the cooker circuit but I know it’s going to be same outcome, smart meter was installed few years ago so can’t blame that. I stay there for about 20 mins each time looking like a fool. Checked every single connection on lighting circuits. I’ve probably found over a 100 faults during past 16 years and I’m struggling in this one. Really annoying me I’m even sleeping on the settee because I’m so restless my mild ocd is bugging me
 
It would bug me too!
Trying to identify if it's truly random, or is more likely at certain times of day might provide clues.
e.g. every time someone connected to same phase takes a shower, or their hot tub stat kicks in etc.

Is there any general rule to how long each episode lasts, and do they settle again fairly quickly or go on flickering for a long time?
 
I’ve disconnected and reconnected everything in the consumer unit, I’ve checked the supply voltage whilst there reading 234v I didn’t believe the customer at first but I asked them to record the flickering which they did and the lights do flicker I’ve supplied them with LED lamps (bulbs) but it still does it. It’s all circuits (down ring)(up ring) have not tried the cooker circuit but I know it’s going to be same outcome, smart meter was installed few years ago so can’t blame that. I stay there for about 20 mins each time looking like a fool. Checked every single connection on lighting circuits. I’ve probably found over a 100 faults during past 16 years and I’m struggling in this one. Really annoying me I’m even sleeping on the settee because I’m so restless my mild ocd is bugging me
I'd try switching on a heavy load like cooker rings and see what's flickering

Usually means it's at the dB or further upstream

I'd be checking voltage drop under load too at outlets see is it dropping at the supply or board
I’ve asked the same questions is it when you’re subjecting power whilst shower is on answer no it’s mixer shower. Then my next question “is it when you’re cooking” answer no it only happens every now and then and not whilst we are cooking baffling me
 
It would bug me too!
Trying to identify if it's truly random, or is more likely at certain times of day might provide clues.
e.g. every time someone connected to same phase takes a shower, or their hot tub stat kicks in etc.

Is there any general rule to how long each episode lasts, and do they settle again fairly quickly or go on flickering for a long time?
Only flicker for a short time
 
I’ve asked the same questions is it when you’re subjecting power whilst shower is on answer no it’s mixer shower. Then my next question “is it when you’re cooking” answer no it only happens every now and then and not whilst we are cooking baffling me

I'd be checking myself anyway

Incandescent is the easiest to see it with

Is it dimming or actual flickering,

The dimming usually indicates the voltage drop

The flickering I'm not sure , maybe that could be indicating an external event altogether

Someone else wiser than me will probably be along with the right answer as usual
 
I'd be checking myself anyway

Incandescent is the easiest to see it with

Is it dimming or actual flickering,

The dimming usually indicates the voltage drop

The flickering I'm not sure , maybe that could be indicating an external event altogether

Someone else wiser than me will probably be along with the right answer as usual
Its a combination of flickering and dimming it’s honestly a difficult one i would normally find the loose connection say thank you very much and walk out the door this one is no loose connection no faulty mcb no faulty rcd no faulty main switch so I don’t know. I honestly don’t know what the next step is other than changing consumer unit first which the customer can not afford so I’m in a difficult situation here ?‍♂️
 

Reply to Lights Flickering in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
446
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
707
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top