Hopefully a picture is attached.

The lights in this house are not on the RCD side of the board, there is a spare way which they could slot into and be protected by the rcd.

The lights are not split up and down so no problem between a borrowed neutral between top and bottom tripping the RCD.

Just wondered what other reasons there were why these would not have been put on the RCD side of the board ?

20190407_113342.jpg
 
Lights were routinely placed on the non RCD side of the board in the past, this was probably due to the fact that when lightbulbs blew they tended to take out the RCD, in a one RCD board this would have taken out the whole installation. As this is an old board this is probably the case.
 
Got to disagree with roly I'm afraid, blowing lamps don't take out the RCD, they take out an MCB, usually a type B MCB because of a current surge. The reason lights were not put on the RCD when that board was installed (16th edition) was that it was not a requirement, the RCD side generally only protected socket outlets. This was the accepted practice.
 
Got to disagree with roly I'm afraid, blowing lamps don't take out the RCD, they take out an MCB, usually a type B MCB because of a current surge. The reason lights were not put on the RCD when that board was installed (16th edition) was that it was not a requirement, the RCD side generally only protected socket outlets. This was the accepted practice.
Usually they don't take out the RCD, but it's not guaranteed. I have had an RCD trip due to a blowing lamp before in my own house. Not sure what came into contact with what causing the imbalance.

But I would agree that it is likely to be a 16th Edition installation where providing RCD protection to lighting circuits was unheard of.
 
Got to disagree with roly I'm afraid, blowing lamps don't take out the RCD, they take out an MCB, usually a type B MCB because of a current surge. The reason lights were not put on the RCD when that board was installed (16th edition) was that it was not a requirement, the RCD side generally only protected socket outlets. This was the accepted practice.
Must just be my customers then, lamp pops, takes out the mcb which then in turn takes out the RCD. Customer then phones electrician as they have reset the mcb and the electric hasn't come back on......?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottingham

Thread Information

Title
Lights not on RCD side of board
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Luke238,
Last reply from
Charlie_,
Replies
11
Views
1,967

Advert

Back
Top