During a heavy rainstorm in the evening, all lights and plugs went out in the living room, adjacent foyer and 3 outside lights (1 near the front door and 2 garage carriage lights). Everything else worked normally.
Next day I did some trouble shooting. No breakers tripped. I checked voltage coming out of each breaker. 120V. I checked the connections in the breakers and on the neutral bus bar. Seemed OK. So I was convinced that I had 120V and good neutral wires leaving the breaker box.
Next I went to the junction box in the living room. No voltage in the junction box. I checked continuity between the breaker output and the junction box. No continuity. I checked continuity between the neutral bus bar in the breaker box and the neutral wire coming into the junction box. No continuity. AZ home. Stucco, Built on slab. No basement.
I'm stumped. HELP.
 
Thanks for your help, but haven't been able to try your suggestion yet. You see the pic of the one living room wall, hours to move all the shelving and stuff away to get to the outlets. There is a second wall, to the left in the one in the picture, that is somewhat similar, that is, massive display shelves full of stuff. But, again, thanks for your input. It's got to be the solution to the problem. I think it's the only thing that makes any real sense.
 
Thanks for your help, but haven't been able to try your suggestion yet. You see the pic of the one living room wall, hours to move all the shelving and stuff away to get to the outlets. There is a second wall, to the left in the one in the picture, that is somewhat similar, that is, massive display shelves full of stuff. But, again, thanks for your input. It's got to be the solution to the problem. I think it's the only thing that makes any real sense.
I’m really pulling for you and I still think it is a receptacle keep in touch please
 

Reply to Lights Out in the USA Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
506
  • Question
It sounds like there is damage to the wiring underground. Do you know what kind of cable was used, in any underground wiring is used has to be UF...
Replies
3
Views
693

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician Laws and Regulations related to Electrics and Electricals within the United Kingdom. Electrician talk, questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top