Got a small job to do this week replacing an existing light fitting for a new customer. Im not familiar with the installation so dont know what sort of state it is going to be in. During my conversations with the customer they have asked for a certificate to be completed for the work. I told them that for such work i wouldnt normally issue a certificate as it falls under maintenance, but if that is what they're insisting on, and me
being keen to impress them, then i will go along with there wishes.

My question to you fellow sparks is how far you would go in regards to the testing and certification for such a small job. I have been told that i am unlikely to be able to gain access into the consumer unit other than to lock off the required circuit. With that in mind my plan was to take a Zs reading at fhe existing fitting prior to removal, so as to probe the means of an effective earth, and then once again when the new fitting is installed.

I was going to detail in the comments section my actions and results prior to removing the old fitting and then record my Zs value of the new fitting in the appropriate column. R1+R2 and IR readings i would detail as a limitation. Obviously i would record all other relevant info such as OCPD and type of earthing arrangement, but with regards to the testing have i done enough/not enough?
 
This is not an alteration to or extension of an existing circuit.
It’s replacement of an item of equipment.
As such most of the tests not relevant.
Yes, conduct a Zs test to confirm CPC continuity, that’s all that’s required.
Oh and no LIM, it’s a Certificate, not a Report.
 
This is not an alteration to or extension of an existing circuit.
It’s replacement of an item of equipment.
As such most of the tests not relevant.
Yes, conduct a Zs test to confirm CPC continuity, that’s all that’s required.
Oh and no LIM, it’s a Certificate, not a Report.
Should i just leave blank the boxes for R1 and R2, IR tests?
 
1) R1+R2 or R2. 2) Insulation Resistance. 3) Polarity. 4) Zs. 5) RCD if applicable. I have an NICEIC 2392 learning guide, which suggests the essential tests are 3, 4 & 5 (5 if applicable) and if reasonably practicable 1 &2. BS7671 only refers to results of tests, as suggested in the model form App.6



From a thread a while back
Is that for an initial verification? Or a situation like im referring to?
 
This is not an alteration to or extension of an existing circuit.
It’s replacement of an item of equipment.
As such most of the tests not relevant.
Yes, conduct a Zs test to confirm CPC continuity, that’s all that’s required.
Should i just leave blank the boxes for R1 and R2, IR tests?
Leave blank, draw a line through the part for the result or write N/A.
Drawing a line would probably be my choice, depending on how I feel.
If you leave it blank, it may be misconstrued that you have just forgotten to enter a value.
 
Got a small job to do this week replacing an existing light fitting for a new customer. Im not familiar with the installation so dont know what sort of state it is going to be in. During my conversations with the customer they have asked for a certificate to be completed for the work. I told them that for such work i wouldnt normally issue a certificate as it falls under maintenance, but if that is what they're insisting on, and me
being keen to impress them, then i will go along with there wishes.

My question to you fellow sparks is how far you would go in regards to the testing and certification for such a small job. I have been told that i am unlikely to be able to gain access into the consumer unit other than to lock off the required circuit. With that in mind my plan was to take a Zs reading at fhe existing fitting prior to removal, so as to probe the means of an effective earth, and then once again when the new fitting is installed.

I was going to detail in the comments section my actions and results prior to removing the old fitting and then record my Zs value of the new fitting in the appropriate column. R1+R2 and IR readings i would detail as a limitation. Obviously i would record all other relevant info such as OCPD and type of earthing arrangement, but with regards to the testing have i done enough/not enough?
You need to ensure the circuit / system you are working on is safe don't you? tell them that you need access to the prperty to do some simple tests.
 
1) R1+R2 or R2. 2) Insulation Resistance. 3) Polarity. 4) Zs. 5) RCD if applicable. I have an NICEIC 2392 learning guide, which suggests the essential tests are 3, 4 & 5 (5 if applicable) and if reasonably practicable 1 &2. BS7671 only refers to results of tests, as suggested in the model form App.6



From a thread a while back

I've given you a disagree because this is a commercial property - if the MCB is on a shared RCD then switching it off to test the RCD may simply be impractical.

Cert needs to read "like for like replacement of light fitting. Test for Zs only"

I normally note the Zs on my invoice - life is too short to do certificates for this sort of work.....

Obviously anything "unusual" should be commented on only ...........
 
To be honest, I really don’t see the point of measuring either R1+R2 or R2 on it’s own in this scenario.
If this were a new circuit, then measuring R1+R2 would (with a known Ze) allow you to calculate whether the Zs would be acceptable once the circuit is energised.
Yes measuring R1+R2 or just R2 will confirm CPC continuity, but then, so would measuring the Zs.
Measuring the IR is another can of worms.
 

Reply to Like for like replacement and MWC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
386
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If this is a genuine change then throw it back at them, a nicely worded email explaining the additional testing requirements and paperwork charge...
Replies
14
Views
2K
  • Question
The legs on the bus bar are too long for the new rcbos
Replies
3
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top