DTM20
Hi,<br> <br>I have had an issue with a supply provided by another contractor. We are carrying out an installation on an extension to an existing building/installation. The other contractor has provided the supply to the new area. On there certificate it says limitation on a few key areas. As far as I understand you aren't allowed limitations on an installation certificate, if this is the case is there anywhere this is written down I can refer to. Also there is a limitation on the bonding connection to the main water. Again I assume this means they can't find it, I'm sure the nic would consider this a major non compliance ? Again is there something I can refer to in writing for this. <br>I sympathise with the other contractor as if is an extremely large building and I imagine the bonding is very difficult to find, however I imagine there is no instance where it is permissible to not verify a main bonding connection.<br><br>thanks in advance
The electrical installation certificate cannot have limitations on it.
Guidance note 3 under "electrical installation certificate" states that and defects or omissions revealed by the inspection shall be made good and inspected and tested again before the EIC is issued.
For bonding if the connection could not be found then testing for continuity and getting a low reading would be a way of testing to be able to expect that the bonding conductor was connected. (though in a large building this result may be suspect because of the likelihood of parallel paths).
However your installation will also require you to test the bonding so it may become moot if you have done this already.
Thanks for the replies gents. I think any responsible contractor would agree the main bonding conductors must be verified. In this case as the supply was provided by others, we wanted their certification to verify the existing installation was satisfactory in terms of bonding, however I suppose this should of been verified at design stage, however this project has been designed by a specialist who I suspect never took the main bonding in to consideration.
First off, it doesn't matter a hoot what the NICEIC think, they don't make the rules!!
You say this is a large building that you are adding an extension too, what are we talking about here an office building, multiple dwelling building, factory building?? Does it have it's own distribution TX, Multiple DNO LV supplies (more than one DNO LV service head)??
It's a hospital with one dno supply to the building we are adding an extension too. I'm sure it's not acceptable to not verify main bonding or have a limitation on an EIC,in anyone's eyes, not just the NIC's. Just wondering what people's opinions are on here, it's always good to get other sparks opinions on matters like this I find :)
The Hospital Engineer (Engineering Manager) will /should be able to officially provide you with this information, as well as any other details of the main electrical distribution system, such a Ze or Zdb values etc...
I may be way off but if the main water was running in to the building in plastic pipe then it would be unable to introduce earth potential. In this case it wouldnt need bonding. Despite what niceic say!
I have written Lim on EIC's before.
For example, working at a large shopping centre in central London where I wasn't even allowed in the switch room to verify supply details.
I would always try and verify main bonding.
Tin hat on.
Well I bought the part p doctor book from niceic book and in ther example of certification I stated .water bonded out of sight under sink, this is in departure is that not what it's for
Eh? any chance of that in English mate? Sorry but it doesn't make any sense
If you are talking about a typical domestic house you may well be correct, but in a multi storey block of flats, or in this case a hospital, the original metallic pipework can very easily become extraneous, from the fabric of the building itself.
Hospitals tend to have a higher requirement with regards to the bonding of metallic services, there are also many more such services that will be found in hospital buildings, medical gases being just one example!!
Hi trev
Had a few beers lol basically the OP was saying that you cant put any limitations on eic but there is a example in the book i.e author of book could not find bonding clamp but had continuity on pipes. So he just wrote his findings In departure, proving the installation is save but not to 17th regs
It will though. In a house it will very likely have earth potential through an Immersion or Boiler cpc. Therefore it will become classed as extraneous even if it itself is not.
That is not really a deviation as such as the regs says bond external or within 600 before branch pipework blah blah and then goes on to say or where reasonably practicable.....
How can a non conductive piece of plastic become an ECP?
I know, it can't :). I stated classed as extraneous (I know it is not really as it is not part of the electrical installation) when really I suppose the pipe work becomes an exposed conductive part when connected through an immersion or boiler, whatever it is classed as, it is connected to earth via cpc. The thing is, it wont meet the criterial of NOT being extraneous on the IR test (>23k), so you would have to main bond it. Well that is how I see it :)
Blimey this has run and run. has anyone actually had a look at an EIC and/or the Schedule of Inspections that goes with it. There isn't anything on either that has anywhere to record a LIM or N/V, unless i have missed something. If i have can you point it out to me please.
Before you all jump the gun, the forms i refer to are the IET model forms, not some made up mickey mouse NICEIC garbage.
Cheers..............Howard
So you'd bond a bit of plastic?
It is not ideal to put limitations on EICs but it would be impossible not to with regards on routing of cables within prescribed zones and erection methods on a original installation, also ( not verified ) should never be used on any inspection with I would be worried if the contractor could not locate main bonding as it would be the first thing I look for on any installation. If the contractor is registered with the appropriate governing body they take responsibility for that limitation unless it's agreed with you In writing .
? If I've done somethng that warrants an EIC I know exactly where my cables runs are and what the erection methods are.
Remember, you're certifying YOUR work.
Have to dissagree with you there jlohm.....so tell me, when installing a new circuit what do you put in the supply protective device characteristics box, if you cant legally access the fuse? And dont say contact DNO, cos they wont have a clue.
How about on a more complicated commercial install with no access to the main switch room, and all you are doing is running out a new lighting circuit from a remote DB, Zdb test fine, continuity to local pipe work test fine?? Maybe your the sort that wants to shut the whole commercial install down to gain a true Ze, if so thats your problem!:yesnod:
I make and design my own certs via word, based on the non-statutory BS7671 standard forms and as such I can put whatever I like on my forms......limitations, N/Vs or even kisses if appropriate...
so there:devil:
Those things should be inspected at first fix stage so that you know they are in the right place.
Don't no what others are referring to, but i'm refering to say, a converted to plastic incoming service pipe where the existing copper pipework is still in place. In situations such as blocks of flats, office blocks and other similar large buildings, (even houses with solid concrete floors) that existing pipework can quite easily remain extraneous via/through the fabric of the building itself!!
I've just done a domestic extension where I felt it appropriate to LIM two lines on the test sheets - seemed daft to not include the only two circuits I hadn't touched (being a PV feed and the cooker feed) so I included them on the circuit list but LIM'd them. Agreed that any new circuit shouldn't have a LIM as if it's been newly installed then it has to be all tested and compliant anyway.
Limitations on electrical installation certificates
DTM20,
Rockingit,