I was called to a single phase installation in a pub as the staff were receiving shocks when touching equipment such as fridges water pipes etc. I located a damaged cable where line and PE conductors were touching and causing 240 volts on the entire earthing system at the installation. In other words there was 240 volts PD between the casing of equipment/ water pipes etc and true earth. This was a TT system where the 100ma RCD protecting the whole installation had been removed at some point previously! The ZS reading I was getting was around 2 Ohms. The mystery to me is why none of the MCBs on the installation were tripping out?
I am probably missing something really obvious. Any thoughts/ ideas would be greatly appreciated.
Many thanks
 
What circuit was the fault originating from???

The only MCB's that would operate by themselves under fault condiitons with an earth fault loop impedance of 2ohms or more would be 6A & 10A, B&C type, and 16A & 20A B type.

The 2 ohms would be too high for any of the other to operate & clear the fault. Whomever removed the RCD is a total idiot that has risked the lives of ALL staff & customers of this pub.

I can only hope you rectified the situation AS SOON AS you found it and it isn't still in this condition!

If you look at the tables in BS 7671 you will see the max values for MCB operation under earth fault conditions.
 
With earth faults, there are those with negligible impedance, and those where there is an impedance.
The higher the impedance, the lower the fault current.
The lower the fault current, the longer the time a CPD will take to operate.
You don't mention what sort of device, or the rating of said device that was protecting the faulty circuit.
It appears likely that the fault had such a high impedance, that the current produced, was not enough for the device to operate.
 
Really boils my **** does this, it's exactly as you describe Mal, some incompetent fool has been in to have a look at this problem decided removal of the RCD was the easiest way out and left it at that.

It's a TT system for gods sake, might aswell just give him an MP5 and send him on his way!
 
it was proably done by someone who drinks down the pub. Yeah nmate, i know how to sort that out.
A decent sparks may well of offered a day rate to find the fault and rectify it, but this bloke just removed the RCD for the cost of or indeed a few pints!

I know a few blokes will moan at me saying this, but if we were to follow E54's advice and install decent earth rods with a stable low value, then this type of incident would be less likely to happen.
 
it was proably done by someone who drinks down the pub. Yeah nmate, i know how to sort that out.
A decent sparks may well of offered a day rate to find the fault and rectify it, but this bloke just removed the RCD for the cost of or indeed a few pints!

I know a few blokes will moan at me saying this, but if we were to follow E54's advice and install decent earth rods with a stable low value, then this type of incident would be less likely to happen.


Well thank you very much Johnboy!! lol!! You know it makes sense!! lol!!:hurray:
 
Well thank you very much Johnboy!! lol!! You know it makes sense!! lol!!:hurray:


i think most sparks know it makes sense, but when there is no specific advice on Ra vales, only very vague guidance, then most people see no reason to acheive low values, when an RCD is protecting the instalation.

Its also a matter of economics, as if say i was to quote ÂŁ100 for just the earth rod alobne, and mr E. Lectrician from down tghe road only charges ÂŁ20 for a rod, that the customer thinks does the same job, then who will win the work?
 
i think most sparks know it makes sense, but when there is no specific advice on Ra vales, only very vague guidance, then most people see no reason to acheive low values, when an RCD is protecting the instalation.

Its also a matter of economics, as if say i was to quote ÂŁ100 for just the earth rod alobne, and mr E. Lectrician from down tghe road only charges ÂŁ20 for a rod, that the customer thinks does the same job, then who will win the work?

I know the problems, ....and TT installations have never been cheap to achieve when done properly!! Even the other way round the problem, is expensive. ...ie, a CU with a 100mA front end S type RCD, with RCBO's protecting all the individual final circuits. At least you'll need 2 RCD devices to fail then!!
 

Reply to Line to earth fault but MCBs will not trip..Why? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
851

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top