Reaction score
0
if 2 panels in a array of 10 was connected the wrong way round after making an extention past a dorma window would i still get a VOC reading ? or wound i get 0 volts ?
am worried roofer put 2 neg ends on the extention
 
You might get a reading but it would be a figure minus the two panels, this happened to me a while ago apprentice did it because the roofer had wired the modules incorrectly and there was 2 male ends the roofer told him it would'nt make any difference if he changed one to a female
lesson learnt : never listen to a roofer unless its about roofs

ie if each panel is 50v you should have a reading of approx 500v voc for the array
if he has put 2 neg connectors it will be minus the number of modules on the extension
ie 2 modules less equals 100v less than the expected voc which would be 400v
 
heres what i think he did
+ from inverter to 1st panel then round the 8 panels as normal so the last panel had a - hanging out he then made up an extention lead across dorma and conected - to - between 8th and 9th panel then 9th and 10th panel conected together leaving a + hanging out of the 10th panel which went back to the inverter which makes the last 2 panels wrong way round . I've got to commission the job tomorrow but scoffold been removed today . What reading will i get on Voc if what am saying above is correct? before i power inverter up ?
 
ie if each panel is 50v you should have a reading of approx 500v voc for the array
if he has put 2 neg connectors it will be minus the number of modules on the extension
ie 2 modules less equals 100v less than the expected voc which would be 400v

Not quite, remove two panels and the Voc will go down by 2 x 50V to 400V
put them in the wrong way round and you have to deduct 2 x 50 V AGAIN

Think of them like battery cells or AA batteries, Take 2 AA batteries 2 = 3V , 1 missing = 1.5V, 1 the wrong way round = 0V

so

ie if each panel is 50V you should have a reading of approx 500V Voc for the array

if he has put 2 neg connectors it will be minus the number of modules on the extension

ie 2 modules less equals 100V less than the expected voc which would be 400V
and 2 mondules the wrong way round equals 200V less than the expected Voc which would be 300V
 

Reply to little worried in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar threads

If the batteries are charged and the house is taking little then the full production of the panels will be dumped into the grid. As you have set...
Replies
1
Views
576
  • Question
thanks, will try that in a few weeks when we're next out in our van
Replies
4
Views
750

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top