whazza22

Are we now classing Neutral as a live conductor?

Reason for this is that on the Scheldule of Items tested (page 4 of Periodic Inspection Report), it asks whether the "insulation resistance between live conductors" has been tested.

Just wondering whether this refers to three phase circuits (L1-L2 etc) or single phase circuits (L-N)

Thanks
 
17 edition exam question
an industrial board supplies
4xtp motors 2xtp+n motors 4xsingle phase ring circuits 2xsingle phase lighting circuits
how many live conductors are there
any help appreciated
 
I got a very similar question when I sat the exam. Just add up the number of line and neutrals.

4 x tp motors = 12
2 x tp+n motors = 8
4 x single phase rings = 16
2 x single phase radials = 4

Total = 40
 
Are we now classing Neutral as a live conductor?

Reason for this is that on the Scheldule of Items tested (page 4 of Periodic Inspection Report), it asks whether the "insulation resistance between live conductors" has been tested.

Just wondering whether this refers to three phase circuits (L1-L2 etc) or single phase circuits (L-N)

Thanks



BS7671 2008:

Part 2 - Definitions....... Live Conductor = A conductor or conductive part intended to be energised in normal use, including a neutral conductor but, by convention, not a PEN conductor.

Regards

Dichroic
 
It's always been a live conductor since I've been doing it...

It's designed to carry current in normal operation, although I do agree with you that unless there is a load connected between line and neutral that no current will flow.
 
Last edited:

Reply to Live Conductors..?? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K
  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
425

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top