I said this before on another thread I am not saying it's right or wrong just this is what the Nikky teach now.
As per Electricity at work regulations," No person shall be engaged in or or so near any Live conductor...." "Unless it is unreasonable in all circumstances for it to be dead".
taking of Zs using probes at non- socket points isn't necessary as it can be gained by calculation, therefore you don't have to test non-socket points with probes, you can use calcs, some may not agree but that is the NICEIC veiw or at least it was last time I was on a course at HQ Dunstable, whether thats an a$$ covering exercise is debatable but that's another discussion
So what about testing Ze - done with probes at the CU (No different to the procedure I described above for Zs).
And before you say Ze can be obtained by enquiry - yes it can - they'll quote you the standard 0.35 or 0.8 - hardly an accurate Zs figure if you then add it to your R1 + R2.
AND....you won't have confirmed that you even have an earth path - everythings been calculated.
Remember, R1 + R2 tends to be tested before circuits are terminated into CU - so what happens if, on termination of the CPC, you accidently tighten down on the conductor insulation, giving a high resistance joint.
Your calculation isn't going to show that up.
I don't care what the NICEIC say - Zs measurement is an important test.
We are supposed to be competent to do this - and, in my opinion, 'live testing' doesn't constitute 'working' live - it is necessary.