At my home the neutral and earth are joined by the cut out fuse.

The neutral goes up to the meter and the earth goes straight to the board.

I can't wrap my head around how the earth and neutral are different?

When the cut out fuse is out ( some one broke the seal along time ago shhhh)

I have continuity on the incoming side of the switch between live and neutral and between the live and earth. And between the neutral and earth.

Is this because the live and neutral are joined in the meter? And because the neutral is also joined with the earth at the cut out fuse?

Its driving me mad
 
Earth and neutral are solidly connected together at the DNO's transformer. In TN-S you will read that as continuity via the distribution cables, but there will be a superimposed voltage due to the current flowing in the neutral from other installations, that may disrupt the meter. With TN-C-S regardless of what other connections exist, there is one in your own service terminal (head) so you will easily read sub 0.1Ω N-E and there won't be any potential difference.

There will also be some kind of a circuit L-N through the meter, as it requires power both in order to function and to measure the line voltage. Exactly how that will show up on a continuity test will depend on the exact circuitry inside that particular model of meter. A traditional induction meter with a rotating disc, you will read the resistance of the voltage coil between L-N. An electronic meter could have a number of different internal power-supply circuits that would give you different readings.
 
Earth and neutral are solidly connected together at the DNO's transformer. In TN-S you will read that as continuity via the distribution cables, but there will be a superimposed voltage due to the current flowing in the neutral from other installations, that may disrupt the meter. With TN-C-S regardless of what other connections exist, there is one in your own service terminal (head) so you will easily read sub 0.1Ω N-E and there won't be any potential difference.

There will also be some kind of a circuit L-N through the meter, as it requires power both in order to function and to measure the line voltage. Exactly how that will show up on a continuity test will depend on the exact circuitry inside that particular model of meter. A traditional induction meter with a rotating disc, you will read the resistance of the voltage coil between L-N. An electronic meter could have a number of different internal power-supply circuits that would give you different readings.
So earth and neutral are the same they just go into different bars in this case...

The neutral is the return path so why does the circuit breaker operate when the earth is turned into the return path in the case of a fault....if they are the same
 
I can't wrap my head around how the earth and neutral are different?
They are both nominally at 0V, and as Lucian pointed out in another post what makes the neutral neutral really is the fact that somewhere it is earthed.

The reason they are separated within most systems, and certainly within any installation in the UK complying with current regulations, is that the neutral is "live" in the sense it carries current during normal operations. So strictly speaking the L is "line" as the one at a high voltage relative to earth, but both L & N are "live" as they carry power normally.

So if you have the neutral go open due to a fault, one end goes to the supply voltage. If that is also used to earth exposed metalwork, then that metalwork becomes dangerous!

That is a real risk with the TN-C-S system you have (TN-C means combined N & E, TN-S means separate N & E) is a fault on the combined N & E section (known as CNE, PME, or PEN) makes the earthed metalwork in a house live. All of it.

In the house that is no real risk if it is bonded to extraneous parts like gas and water pipes, as all are at similar potential so you don't touch a dangerous difference inside. But outside it is a different matter and every year there are a few incidents reported to HSE due to this. The risk being greatest for some special cases like hot-tubs or electric cars where people might be wet and in contact with the true Earth as well as the metalwork.
 
A direct live to N connection will give a slightly bigger bang than a live to E connection.

Due to the N cable being. Thicker
 
MCBs are in the line. They will trip just the same whether a fault is to neutral or to earth, they can't tell the difference. RCDs monitor the line and neutral, and trip if there is a difference in the current between them. Although neutral and earth are the same conductor as far as the service terminals, they are separate conductors by the time they reach the consumer unit and RCD. Therefore the RCD can sense whether some of the line current is not returning to the service terminals along the neutral (which must then logically be going to earth, either the CPC or the mass of earth)
 
The neutral is the return path so why does the circuit breaker operate when the earth is turned into the return path in the case of a fault....if they are the same
The RCD look at the difference between the L and N on the load side. A return current (leakage, shock from touching live, etc) back to the N at the supply side, or to true Earth, will cause an imbalance and trip the RCD.
 

Reply to Live earth neutral and the cut out fuse in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top