Evening everyone,

I had new one today, a live neutral terminal on the connector of a LED emergency bulkhead. This fault repeated on 4 other units.

The neutral was being taken from a 4ft fitting next door that a new guy had been messing around with.

Any ideas why or how?

Cheers
1000042562.jpg
 
A N terminal will always become live if the following are true

Live is connected to to corresponding live terminal of the load
The load is switched on
The N terminal has become disconnected from supply N.

Watch out, one of the floating N cables is likely to be live as well.
 
Looks to be a loss of the Neutral, I assume the fitting wasn't working.

If you disconnect N from an energised working circuit, you would expect to see voltage on the N connector of the fitting.

Leaving hanging conductors like that isn't a good idea either.
 
Last edited: