Evening all
Anyone any ideas on a voltage being present on pipework in a flat?
All bonding done and satisfactory Ze at board.
It’s a block of 3 which I’ve isolated all Power to two of the flats the third is a holiday home which I can’t access. I was thinking there is an issue either in the inaccessible flat or an external problem. Any ideas would be appreciated. The incomer to the two I can access is a tn-s 3 phase.
Cheers
 
possible fault current flowing to earth through the pipe?. could be that the fault current is not sufficient to trip any protective device fitted?
If the pipe runs through the building then the fault could as you said be in any of the flats??
Are you able to access the cutouts for other flats? came across a similar on a TT once where the rod was disconnected as somebody stole the cable! and system was using water pipe as the main earth.
have you fully checked all the bonding and that the necessary clamps are all secured properly?
 
Last edited:
If Ze and bonding are ok then there can't be much voltage on the pipes, surely? Need a lot of current to generate a potential across 10m of 10mm (say) and that should trip any RCD and probably the circuit breakers too?
 
Was measuring 48 volts using mft. I have measured ze at cut out in flat. The cut out in flat is tapped off the 3 phase tns at entrance stairwell to two of the flats. Im heading back tomorrow to make sure I’ve not missed anything stupid, cheers for replies so far.
 
I would suggest you check the Ze at the DNO head with all paths removed.

I had this once and it was a dodgy TN-S and a R1+R2 link left in on another flat.

The funny thing is because I reported the poor Ze to the DNO when they put a PME link and everything was sorted I thought no more of it.

It was two years later when I went to test a different flat and spotted the R1+R2 link left in that I put 2 and 2 together. Clearly when the DNO sorted their earth out it tripped the MCB in the flat with the fault as it should have.
 

Reply to Live pipework problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Written in clauses are essential, but should be fairly standard fare to a solicitor. A similar situation exists around where I live with regard to...
Replies
9
Views
596
  • Question
Thanks. I do a lot more for the site than just change a few alarm batterys. EICRs, PAT, numerous little jobs. Never away from the place.
2
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top