Evening all
Anyone any ideas on a voltage being present on pipework in a flat?
All bonding done and satisfactory Ze at board.
It’s a block of 3 which I’ve isolated all Power to two of the flats the third is a holiday home which I can’t access. I was thinking there is an issue either in the inaccessible flat or an external problem. Any ideas would be appreciated. The incomer to the two I can access is a tn-s 3 phase.
Cheers
 
It is looking like a neighbouring property that is a holiday home so this could drag on. The dno isolated as many properties as possible and the fault was still there. Dno engineer said he would phone me back which will probably be tomorrow.
 
Evening,
I have just found a problem that I had with taps giving us a little buzz every now and then, but not enough to trip the RCD's in the CU. I found we had an intermittent 22v coming through the main earth on a TN-S system. I found the 22v by checking the bonding and then measuring between the MET and the main earth. To cut a long story short, it was a fault in the street lights outside that was sending voltage to the earth at the transformer down the road.
 
Evening,
I have just found a problem that I had with taps giving us a little buzz every now and then, but not enough to trip the RCD's in the CU. I found we had an intermittent 22v coming through the main earth on a TN-S system. I found the 22v by checking the bonding and then measuring between the MET and the main earth. To cut a long story short, it was a fault in the street lights outside that was sending voltage to the earth at the transformer down the road.
Earth fault voltage from outside the installation will not trip RCDs inside the installation.
 
Did hear a story a few years ago about the gas engineers that go a shock when cutting a gas pipe as the home owner bypassed the meter and stuck the neural able to the gas pipe, may be an "Urban Myth"
 

Reply to Live pipework problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Written in clauses are essential, but should be fairly standard fare to a solicitor. A similar situation exists around where I live with regard to...
Replies
9
Views
588
  • Question
Thanks. I do a lot more for the site than just change a few alarm batterys. EICRs, PAT, numerous little jobs. Never away from the place.
2
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top