Good evening,

a colleague of mine wants to install a sub main into the liveside of a mainswitch in another board.

Can people please provide me a answer if it ok or not

thanks
 
Too many variables to give a reliable answer.
IF the main switch terminals are designed to accept two conductors, and IF it is already fed from a submain and The new cable is the right size for the OCPD of that submain. Also if that existing submain has spare capacity to feed this new submain then it might be ok.
 
Thanks for the reply

The board is a small board 63/100 amps fed from around 60/70 meters away.
the supply for the new board is 63 amps.

Personally I think it shouldn't be done but designer said it is ok
 
Not really, you should have a single point of isolation, and whilst it may be possible to fit two sets of tails into the switch (2X25mm² is a bit tight even on a 50mm² capacity terminal) it is not good practice.
Use an isolator and a Henley block.

You're assuming its a 100A board at the intake then?
If it's already fed via a submain then it is possible.
 
You're assuming its a 100A board at the intake then?
If it's already fed via a submain then it is possible.

It will be coming from a large board located in switch room cannot gain access at the moment

Richard it is been added onto the plans so we will be covered but I am questioning it because don't each circuit need a way of isolation
 
so is the existing cable suitable for the added design current of the new board? What about terminating the existing into a switch disconnector and then taking two feeds to the separate boards?

The cable is should be suitable as we need 63 amp supply
I think I will advise the disconnector option as the small board they want us to come off is redundant
 

Reply to Live side in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
637
  • Question
Jumping on and off jobs can be tough going when you're less than confident as every time you go back it's like a new job. that you know little...
    • Like
2
Replies
15
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top