live Zs readings | Page 2 | on ElectriciansForums
Discuss live Zs readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
i wonder if he as popped the HRC fuse ?? if he as tryed to use the 2 leads for IR and Low ohms settings and used them on loop Ze/Zs reading ...
Meggers i think have a high and low test.
Hi test requires N&E together and line.
Low test requires LNE connected to each respective terminal.
quite true, but on both settings you wont get a reading for zs without 3 leads connected (unless my meg is a knackered one)
Standard loop impedance test (can't think is it 23A or 26A?) for Megger only requires two leads connected to line and earth respectively.
Only no trip (15mA) test requires three leads.
I knew what i meant :D
Also, you will be surprised at the different readings you get between high and low tests at the same test point.
If anyone is interested as to why the readings differ it's because the no trip (low) test uses a very short pulse and the RCD has significant inductance, so the observed figure is higher.
hi everyone been using my kewtech kt64 today and have had problems when testing a live zs on the upstairs and downstairs lights both tests where tripping the main breaker so i didnt carry out the test. can anyone explain? (all othere live zs was fine)
Is it perhaps a 6A Type B BS EN 60898 circuit breaker?
It should trip instantaneously between 18A-30A. Earth fault loop impedance test is within this range.
If you can't do low-current test then you'll need to calculate Zs.
Reply to live Zs readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...