Could anybody tell me if this seems to make sense.
60Amps x 230volts = 13800Amps or 13.8Kva (per apartment)
The landlords supply would be negligible with only LED lighting and power to standby batteries (fire alarm)
But say
5Amps x 230 volts =
1150Amps or 1.15Kva
Therefore a total of
(13.8x4) + 1.15 = 56.35Kva
This is pretty much purely academic as the above is the calculated value but the network provider will allow for diversity (I.e. not everything being used simultaneously) and therefore probably only provide a 5.5Kva supply at street connection.
They should really know this as it is only a domestic situation. Hope this makes sense.