where abouts are these ryefield boards going to be located?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Location of PME Links in the Commercial Electrical Advice area at ElectriciansForums.net
Sorry for the delay, been away for a bit.
The landlords DB's are also every 3 floors, for corridor lighting and sockets, stairway lighting and what have you. These are fed by busbar trunking, Tapped off every third floor. This is because the Landlord's power requirements is not so substantial. But to supply 400 flats off of busbar trunking (that's 400x100A fuses), is going to be very expensive. Space is tight in the risers, so forget about putting multiple busbar trunking, it takes up too much room.
At each Ryefield board, there will be a maximum of 30 flats being supplied. That's 10x3c25mm cables out of the header trunking, running up the riser to the floor above, 10x3c25mm cables out of the header trunking and out through a letterbox to feed this floor, and 10x3c25mm cables from the bottom of the ryefield board and down to the floor below.
Each header trunking is over 150mm2 and over a meter long. Each Ryefield board is about 600/700mm wide and about 1000mm in height.
Just done a search and Eaton's range only goes up to 6300A, shneiders to only 5000A.
So we are talking about 6 or 7 busbars to feed that lot. Just isn't the space for that.
Sorry for the delay, been away for a bit.
The landlords DB's are also every 3 floors, for corridor lighting and sockets, stairway lighting and what have you. These are fed by busbar trunking, Tapped off every third floor. This is because the Landlord's power requirements is not so substantial. But to supply 400 flats off of busbar trunking (that's 400x100A fuses), is going to be very expensive. Space is tight in the risers, so forget about putting multiple busbar trunking, it takes up too much room.
At each Ryefield board, there will be a maximum of 30 flats being supplied. That's 10x3c25mm cables out of the header trunking, running up the riser to the floor above, 10x3c25mm cables out of the header trunking and out through a letterbox to feed this floor, and 10x3c25mm cables from the bottom of the ryefield board and down to the floor below.
Each header trunking is over 150mm2 and over a meter long. Each Ryefield board is about 600/700mm wide and about 1000mm in height.
Just done a search and Eaton's range only goes up to 6300A, shneiders to only 5000A.
So we are talking about 6 or 7 busbars to feed that lot. Just isn't the space for that.
nothing to be confused about he is "mad dog murdoch"I'm still a little confused on a few things, the main worry being as to how these 3 X 30 way Ryefields are being connected to the 185mm 4 core cables?? Surely they aren't being in and out connected off the Ryefield bus bars, because if they are, unless i'm missing something at least two of those 3 Ryefield panel bus bars are going to be potentially over loaded!! They will be carrying the load (which they were not designed or sized for), from the other Ryefield panels, as well as it's own supplied load....
I'm still a little confused on a few things, the main worry being as to how these 3 X 30 way Ryefields are being connected to the 185mm 4 core cables?? Surely they aren't being in and out connected off the Ryefield bus bars, because if they are, unless i'm missing something at least two of those 3 Ryefield panel bus bars are going to be potentially over loaded!! They will be carrying the load (which they were not designed or sized for), from the other Ryefield panels, as well as it's own supplied load....
If it wasn't the xmas hollidays you'd have them already. Not back for another week but I'll post them as soon as I can.
Reply to Location of PME Links in the Commercial Electrical Advice area at ElectriciansForums.net