Hi guys, quick question
looking at getting around to installing a loft light at my sisters house and the board is 16th edition lighting on non rcd side. Cables will be clipped to wood work but 1 foot and half roughly will be going between joists to landing light. In this bit it is boarded and I was thinking about leaving on non rcd side, but thinking as the joists are about 75mm do I need to put on rcd side? As I look at on site guide it states cables passing through joists are to be plus 50mm and cables in walls or partitions need to be 50mm plus but as I am running between 2 joists ina ceiling and not passing through any joists to landing light do you think this needs rcd protection as the way I interpret it there are 2 sets of rules for cables in wall and other in ceiling and the rules don't state in a ceiling if rcd is needed when cables run along joist. Or should I take the plus 50mm rule when cable I talked in wall or partition?
Sorry for a silly question but looking to do the best way.
Cheers
APE
 
Again, RCD protection for cables above ceilings and below floors is not an acceptable method for providing additional protection.
An acceptable method would be to notch the top of the joist, and then cover the cables with 3mm steel plate.
Another thing to consider, is the depth should include the lath and plaster and floor boards (if there are any).
 

Reply to Loft light cables in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
357
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
910
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
393
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
666

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top